Hi all,
Customer wants to install a holiday home in one of their fields 300m away. They want a 63amp supply so I just ??
Quick calc comes out at 95mm swa not sure what size drum it would need. I suggested they should ring sse and get a quote for a new supply of off the power pole at the house
Can anyone think of install ideas
Thanks
 
63A? Most holiday homes, static caravans of old along happily on 16A…

32 for one of the double unit lodge type.

I suppose, if they’re future thinking of a hottub or car charger at the holiday home, they might need 63A
 
Complying with 3% volt drop from origin for lighting is going to be expensive or not going to happen!
(It's a I shame we can't go back to the ?15th edition which I think said just the final circuit had to comply)

I'd be inclined to get very rough cable quotes for 300m of 95mm, 50mm and 25mm SWA (for 63A, 32A and 16A supplies respectively). 2 Core and TT might save a bit (I honestly can't remember what section 7 requires for a static caravan). The bonding requirements need thinking about too.

The cable prices alone may prompt reconsidering gas cooking and heating or even a different unit! Two Calor bottles with a changeover valve last a very long time.
 
I am not up on the current legislation concerning holiday homes, but it used to be that they can only be occupied for X amount of months during a year and not have a permanent power supply, this may have changed since I was involved in this type of development.
 
I am not up on the current legislation concerning holiday homes, but it used to be that they can only be occupied for X amount of months during a year and not have a permanent power supply, this may have changed since I was involved in this type of development.
That may be true as the suppliers have asked for 63a commando skt so they can just plug in
 
Realistically 5% is fine these days for LED lighting.

Going TT would save a lot more in cable than it should cost in up-front delay RCD!

Also might be worth looking at larger aluminium cable for same drop but lower cost (Al needs about 50% more than Cu, so around a size up). But remember the serious issues of galvanic corrosion so it might be worth getting some resin filled cable joints at both ends to change down to 25mm copper for ease of wrangling.
 
For example, using paralleled cores of this 4-core 70mm aluminium stuff:

At the princely sum of £10.18/m + VAT, compared to £19.98 for copper 95mm:
 
The talk about caravans being used for only part of a year is a license stipulation of the caravan park it is sited on. In this case, no licensed park, so it doesn’t matter.

New holiday homes by people like Wilkerby, ABI, etc make holiday homes to two British standards. Actual holiday homes, and “residential” homes which are built to a higher spec and are designed to be lived in all year.

either way, they tend to come prebuilt with gas central heating and cooking… unless this is being built to a customer spec
 
Holiday cottage owner here! To qualify as a holiday home (business rates rather than council tax) it has to be available for letting for at least 210 days per year.
There's also a maximum consecutive letting period to one individual or group of guests. I forget exactly how long this is, but a few years we had someone rent a cottage for ten weeks while they bought a house in the area, which was legal. The house purchase fell through at the last moment, so they wanted to stay on for another four weeks, which, strictly speaking, they shouldn't have.
 
Just make sure that the devices that this cable is connected to are also rated at 90c then all is well.
In this case you can safely ignore the 90C rating as the size of the cable is down to volt drop.

For example the 95mm XLPE 90C SWA cable is rated at 239A (Table 4E4A, method D) so at 63A your I2R loss is just over 14 times lower, so your table values for 20C ground -> 90C insulation rise scaled to that will be of the order of 5C (i.e. cable runs at 25C is in duct in ground at 20C).

Wrangling and terminating 95mm on the other hand is a serious issue!
 
In this case you can safely ignore the 90C rating as the size of the cable is down to volt drop.

For example the 95mm XLPE 90C SWA cable is rated at 239A (Table 4E4A, method D) so at 63A your I2R loss is just over 14 times lower, so your table values for 20C ground -> 90C insulation rise scaled to that will be of the order of 5C (i.e. cable runs at 25C is in duct in ground at 20C).

Wrangling and terminating 95mm on the other hand is a serious issue!
Interesting.
Yeah been a long time since I've worked with 95mm and above. Sure I can dig out my old club hammer to help with termination ?
 
Wrangling and terminating 95mm on the other hand is a serious issue!
I actually have 95mm2 SWA as a submain to my own house. Not chosen because it was required, but because a supplier delivering a reel to a job I was doing damaged the cable, leading to me rejecting it.
Replacement was delivered to site, but the damaged cable not removed, so an undamaged section ended up feeding my house.
It terminates into a surprisingly small galvanized adaptable box with crimped lugs on the conductors. 25mm2 tails are also fitted with crimped lugs, and the pairs of lugs bolted together before the box was resin filled.
 
Interesting.
Yeah been a long time since I've worked with 95mm and above. Sure I can dig out my old club hammer to help with termination ?
I don't normally work with anything big, so last year when I had a job that might need it I bought just 1m of the planned cable to get a feel for what I might be getting myself it for and to check the glands would fit properly, etc.

Can't imagine what the postman though of it!
 
It terminates into a surprisingly small galvanized adaptable box with crimped lugs on the conductors. 25mm2 tails are also fitted with crimped lugs, and the pairs of lugs bolted together before the box was resin filled.
Interesting, though in my case the tools I have only crimp up to 50mm so would have to think about borrowing/renting something for above that.

The likes of the Al cable are sectorial, presumably you get special quadrant shaped crimps for them?

If cable cost were the driving factor for the OP I would be looking at the 70mm 4-code aluminium option with some sort of resin filled termination, probably going to 16mm 4-core copper and then finally pairs of the 16mm to terminals indoors so you can IR test each core separately.

Based on the illustration here, for minimum inductance factor I would pair opposite cores, so brown & grey for L and blue & black for N for the cable:

While it might need to be TT if a caravan like metal building, for a house it will probably need to be considered the same for supply Zs being too high so still a delay RCD up front at the outbuilding CU. However, the data for 4-core 70mm copper has the armour down as 131mm CSA so above the 10mm copper equivalent needed for extraneous bond TN-C-S so could supplement any local earth rod OK and keep the Zs down far lower than just a rod or two.

I guess it would meed the end of cable Zs for a 63A fuse on 5s disconnection but not checked that, really would need a check for the actual cable armour R2 and supply Ze.
 
If cable cost were the driving factor for the OP I would be looking at the 70mm 4-code aluminium option with some sort of resin filled termination, probably going to 16mm 4-core copper and then finally pairs of the 16mm to terminals indoors so you can IR test each core separately.
Really it should be 5-core 16mm, so there is a copper CPC linked to the major cable's armour to keep the overall path above 10mm if TN-C-S is considered (or even just marginal on the supply fuse end-of-cable Zs limit).
 
300m of 95mm2 2C SWA should weigh about 1000Kg, so no big problem at all for the type of gear found on a farm. I used a small trailer with the reel threaded onto a length of steel bar tied across the top of the trailer sides.
95mm2 SWA isn't as big as some of you are thinking.
 
Something I’ve long wondered - can this amazing toy also lay cable or would it end up too near the surface?

Never used one, but the required depth for laying pipe is every bit as much as for cable, so the answer is yes. The warning tape would be the problem.
We have a 400m long service pipe to our property, which sprung an expensive leak about three years ago. The pipe is 60 years old, so I was looking at these machines with a view to replacing it, but in the end the leak was easily found, along with the reason for it, so it was just repaired.
 
It looks like the design of the shepherd's hut is the problem, if they think they need a 63A supply. Too many instantaneous water heaters with no allowable diversity I suspect.
I have a as yet unused (and possibly never to be used) site for a shepherd's hut to complement my holiday cottages, but I did some design work on it, and it's possible to be all electric and run on a supply of 6kW.
 
It looks like the design of the shepherd's hut is the problem, if they think they need a 63A supply. Too many instantaneous water heaters with no allowable diversity I suspect.
I have a as yet unused (and possibly never to be used) site for a shepherd's hut to complement my holiday cottages, but I did some design work on it, and it's possible to be all electric and run on a supply of 6kW.
Yeah I think 63 is too much but they have spec 9kw shower, heating, range style cooker
 
Loose the instantaneous shower, and fit a 3kW pressurised storage cylinder. Feeds the sink and basin as well, and gives a far better shower than any instantaneous one. Arrange cooker to load shed both the water heater an the room heating when in use. Water heating off for a while won't matter, and if a cooker is pumping 6kW of heat into the hut, they won't mis the heating either.
2kW should be more than enough fixed heating for an insulated hut, but a 2kW portable heater can be provided as well for exceptionally cold weather, and just plug into the socket circuit.
 
Loose the instantaneous shower, and fit a 3kW pressurised storage cylinder. Feeds the sink and basin as well, and gives a far better shower than any instantaneous one. Arrange cooker to load shed both the water heater an the room heating when in use. Water heating off for a while won't matter, and if a cooker is pumping 6kW of heat into the hut, they won't mis the heating either.
2kW should be more than enough fixed heating for an insulated hut, but a 2kW portable heater can be provided as well for exceptionally cold weather, and just plug into the socket circuit.
Thanks the customer has obviously outsourced the hut to a specialist company but saying that they are a new start up so will pass on some ideas for her to forward on to them. May even become their recommended installer ?
 
Good luck for the project, hopefully you get it and can let us know how it all pans out.

One aspect to consider carefully is the supply access, and if this holiday home would ever be used while the main home owners are away. As it is TT, the SWA will need a 100mA or 300mA delay RCD before it (as well as a fused-switch or similar for OCPD, more to protect the home main fuse and assuming it is 100A otherwise no usable selectivity).

To make sure that delay-RCD is very unlikely to trip you should plan on using a CU that has double-pole RCD on all circuits. Even cheap dual-RCD boards do that. But given the overall cost already and the benefits of easier fault isolation, etc, I would suggest an all-RCBO CU, but then look for the RCBO that are neutral-switching so you don't end up with a N-E fault taking out everything. The recent compact RCBO from Fusebox, Wylex, and Crabtree all seems to be DP switching and are reasonably priced.

Don't forget to include SPD. I think some of the CUs come pre-fitted anyway, such as this:
If the main home is feed from overhead lines it might be worth checking it already has SPD, or maybe making the recommendation that they should consider adding some.
 
Never used one, but the required depth for laying pipe is every bit as much as for cable, so the answer is yes. The warning tape would be the problem.
We have a 400m long service pipe to our property, which sprung an expensive leak about three years ago. The pipe is 60 years old, so I was looking at these machines with a view to replacing it, but in the end the leak was easily found, along with the reason for it, so it was just repaired.
They are quite good , but that particular one would probably only manage a depth of around 400mm and not the required 1000mm
Across productive agriculture land.
But even with a more substantial mole and blade along with a machine somewhere in the region of 10 times the horse power of the one in the picture , unless you can 100% guarantee no stones or sharps in what you are moleing , I would not want to put my name and liability to the job.

As a company we generally install 3 or 4 runs like this a year , the largest we have done from memory was around 780m.
It is all about having correct kit , and at a push can be carried out single handed , but is a obviously a lot quicker and more straight forward with a 2 or 3 people.
What ever you do , always lay and never pull a cable of this length.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Forest electrical

Thread Information

Title
Supply feed to holiday home
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
39
Unsolved
--

Advert

Thread statistics

Created
sclarkin,
Last reply from
JD6400,
Replies
39
Views
5,223

Advert

Back
Top