Hi Guys
I have been asked to quote for putting in a supply to a pair of steel site cabins on a construction site.
At the minute there is no electrical supply to the site but there is a proposed position between the two cabins where the supply will be (there is a surface mounted meter box on the wall). The most each run of cable will be is 13 meters. i was plannning on using 4mm 3core armoured for each. Can the armoured come straight out of the main switch / isolator that the electric board supply, or will that need protected by a RCD? I will of course be using the 3rd core as the earth and bond the armourings at the glands
Also Reg 704.411.3.1 says a TNC-S system shall not be used for the supply to a construction site, except for the supply to a fixed building. I appreciate that the buildings are not fixed - but they wont be moved until the site is closing. The same rule in 7671 has a note that ESQR prohibit the use of a TNC-S to a caravan or similar! Does this mean that i need to use an earth rod and make it TT?
I am also trying to understand reg 704.411.3.2 does that mean the supply for the cabins would have to come through a 500mA RCD? If i need to put a 2 way RCD board in, i will struggle for space in the meter cabinet, and i know that the builder will not go for the expensive option of another housing
One more question (sorry!), on the cabins, i need to install a pair of 70w Son lights, i was planning on just using flex tie wrapped where possible - the cabin itself is an upstairs one so will not be used for storing stuff of top and the cable is not likely to be damaged - or should i put it in PVC conduit / or Kopex etc? I know i cant drill into the cabin as the hire company will charge the builder for any damage to it, which is why i thought that i could use tie wraps where possible!
Any suggestions will be greatly received as times are tough and i would like to get the job if possible!
Cheers
I have been asked to quote for putting in a supply to a pair of steel site cabins on a construction site.
At the minute there is no electrical supply to the site but there is a proposed position between the two cabins where the supply will be (there is a surface mounted meter box on the wall). The most each run of cable will be is 13 meters. i was plannning on using 4mm 3core armoured for each. Can the armoured come straight out of the main switch / isolator that the electric board supply, or will that need protected by a RCD? I will of course be using the 3rd core as the earth and bond the armourings at the glands
Also Reg 704.411.3.1 says a TNC-S system shall not be used for the supply to a construction site, except for the supply to a fixed building. I appreciate that the buildings are not fixed - but they wont be moved until the site is closing. The same rule in 7671 has a note that ESQR prohibit the use of a TNC-S to a caravan or similar! Does this mean that i need to use an earth rod and make it TT?
I am also trying to understand reg 704.411.3.2 does that mean the supply for the cabins would have to come through a 500mA RCD? If i need to put a 2 way RCD board in, i will struggle for space in the meter cabinet, and i know that the builder will not go for the expensive option of another housing
One more question (sorry!), on the cabins, i need to install a pair of 70w Son lights, i was planning on just using flex tie wrapped where possible - the cabin itself is an upstairs one so will not be used for storing stuff of top and the cable is not likely to be damaged - or should i put it in PVC conduit / or Kopex etc? I know i cant drill into the cabin as the hire company will charge the builder for any damage to it, which is why i thought that i could use tie wraps where possible!
Any suggestions will be greatly received as times are tough and i would like to get the job if possible!
Cheers