i would use a tt system
100ma time delay rcd on the db circuits
Ok Just incase there is any confusion, for the benifit of the OP.
Incoming supply in TNC-S, Have you verified this?. this stands for Terra Neuteral Combined- seperate. So the Earth uses the neuteral onductor to complete the eart fault loop, if anything was to happen on the site then the fault current could be induced into surrounding installations under certain conditions. as per a pme arrangement.
So, use the incoming TNC-S to protect the SWA in the installations but do not connect the earth from the SWA to the boards in the cabins, drive a eath stake in the ground for each cabin and connect this to the MET for the cabin. beware that the ZE for the TT system needs to be less than 21 ohms so be prepared to drive in more than one per cabin.
I would not suggest linking the TT of both cabins as you would have to install some kind of mechanical protection to protect link cable, it would be far easier and far cheaper to just install dedicated rods.
Thanks for that chaps, that has certainly helped! It was the customer who told me that the supply would be TNCS, and it will be in by midweek so i will know for sure by then. I was only asked to quote for the job yesterday and had no time to contact the supplier!
Sorry if the questions seemed daft, but i would rather do the job right and agree with the principle - ' if you are not sure - just ask! '
tt system must have rcd
time delay otherwise it will trip with the 30ma or instead of the 30ma
wouldn't use tnc sSwa is protected by the TNC-s arrangement, the cabins have 30ma RCD to protect the TT side, so i still dont see why we need the TD- RCD??
wouldn't use tnc s
turn to tt system at meter not at cabins.
wouldn't use tnc s
turn to tt system at meter not at cabins.
For TT system all circuit must be protected with rcd.Even if you TT at the incoming why would you want to fit a 100mA S type up front RCD to protect the armoured sub mains? The boards in the cabins protect all the final circuits with a main 30mA one.
Plus as you will have the problem of where your MET will be. As your runing 2 sub mains your MET will have to be at the origin of the installation and so at the head. Which means you either have to use a combined CPC/Bonding conductor in the SWA and may need a larger cable or run bonding conductors back to the MET from the cabins.
I would TNC-S the SWA and then local fit rods.