supply for hot tub and garden services | on ElectriciansForums
Discuss supply for hot tub and garden services in the UK Electrical Forum area at ElectriciansForums.net
Essex
been asked to install a supply to a hot tub.
old one that is there has been fitted to a board in a shed.
the feed to the shed db is 2.5mm then at the house 6mm.
there is no power there due to tripping.
i want to install a new supply and get rid of all that.
they may be getting rid of the shed and asked for the new board closer to the tub area.
so a ip65 cabinet will be fitted.
my confusing is that the house db has a spare rcd way.
i was thinking of running a swa to a sub board with just a main switch and mcbs and relying on the house rcd to proctect.
reason for the board is they what the sockets and shed to still work.
the earthing is a TN-S setup.
in my head i cant see why its a problem as its still being protected by a rcd.
Will I have to up the cable size from 10mm to 16mm?
What makes you think you would need 16mm - how long is the run? and whats the anticipated load of the hot tub and other devices?
AND watch out for the cost of IP rated cabinets for the garden CU. Decent ones cost and what would you plan to attach it to?
Been asked to have a 25a trip fitted so that 32a cos you can't get them.
The sockets will be a radial so 20a if that
And then the shed couple of sockets and 3 lights.
Run to the proposed area roughly 30m
As Tel has said, sooner or later the hot tub ++ will start tripping and some house circuits will be affected. There won't be any discrimination between the house CU RCD and the remote RCD, wherever it is put. So if you have decided the remote hot tub is ok to run on TNS and you can't do the high integrity rearrangement Tel has mentioned, then I'd think about cheap and cheerful just using that spare way perhaps?
I am thinking of fitting a 63A fused unit in and running to the new board
There is a Henley block there
Will make the out side separate from the house.
That was my first thought
There is a spare way in the board
Run off that too the new board and rely on the house rcd
Interesting thread. Me thinks if a diy'er came on asking similar questions they would be told to get an electrician involved.
IMHO people shouldn't be designing a new circuit via an Internet forum; by all means do the calcs then ask on here if it looks correct ( I appreciate not all sparks have to regularly do instal design so get rusty on the calcs side of things).
Just a thought!
Reply to supply for hot tub and garden services in the UK Electrical Forum area at ElectriciansForums.net
Personally, I would take a Ze measurement myself rather than rely on someone else's maybe drive by scrap of paper.
2 3
Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...