Hi guys, when you come across a 100A supply fuse with 16mm tails how do u code it ? Read threads saying that if it is adequate for the load and by using the adibiatic equation we can prove earth is adequate to clear fault what would you do ? Is it a straight case of current carrying capacity < fuse so fail ! Or is there more to it ? What code for 6mm bonding 16mm earth ?? . What sizes were used under previous editions pre 16th ?? And how does this fit in ?
 
and just because it says 100A on the fuse holder, don't mean it's a 100A fuse inside. DNO is not ronseal.
 
6mm and 16mm would be a code 2 as I don't believe u can use the equation on the bonding. But what if the earthing conductor was oversized in the first place and could be 10mm. The main fuse is a different story, firstly we can't cut the seal so can't confirm fuse size ? If we could confirm 60A and it was a small board where the loads were protected by the OCD and the total load couldn't exceed the capacity of the 16mm ??. I don't know
 
Thanks Julian , I'm pretty sure that's the article I had read. So to summarise 16mm 10mm earth would be fine on most installations with 100A fuse providing the conditions stated are met. Thinking the 6mm bonding could be a code 3 actually depends , what if it was installed at an earlier edition then the tails were changed later but not the bonding ?
 

Reply to Supply fuse and tails in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
684
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
969

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
481

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top