1Justin

-
Arms
Joined
May 20, 2011
Messages
497
Reaction score
169
Location
Surrey
My customer needs bigger than 60A supply. Currently BS1361 60A. 4 bedroom house, 4 kids, new circuits..

Before I started in the place it came up at 72A (with diversity), and after my 2 new circuits I am 79A (with diversity). PME, nice condition, modern supply cable, Ze 0.27 so should be able to take 80A fuse).

Given the additions, however I look at it and use diversity I need 80A.

Since I'll be inspected on this job (Mr NICEIC etc), I am sure this needs to be shown to be all ticked off OK. The quote from SSE is ÂŁ131.42+VAT to upgrade the fuse. Surely all they are likely to do is confirm Ze, check the supply cable and earthing conductor, and change the fuse. (modern cable and 16mm main earthing conductor).

Is this a typical quote? I haven't told the customer yet but he's not going to like it given that in his eyes he gets nothing for it.

Is someone here now going to tell me that they just change the fuse anyway without informing DNO? DNO never seem know what the fuse rating is anyhow when I've asked them before.

Justin
 
Wow such a lot of responses. Thanks. All confirming my own opinion really.

What I was trying to do was cover myself for the question Mr NICEIC might inevitably ask me. I was hoping to have a robust response up my sleeve.

As TopCat says:

"If asked by NICEIC inspector what method did you use for working out the estimated load say "the common sense method", you may even get a smile!

If I can "pass" an inspection under this sort of hand-waving policy than that's fine by me. It's not the way we've been taught to behave but I do see how classroom and reality are not always the same thing.

I'll give SSE a call anyway and ask if they'll l get me an 80A fuse for free, no harm, asking.

Rgds
 
My customer needs bigger than 60A supply. Currently BS1361 60A. 4 bedroom house, 4 kids, new circuits..

Before I started in the place it came up at 72A (with diversity), and after my 2 new circuits I am 79A (with diversity). PME, nice condition, modern supply cable, Ze 0.27 so should be able to take 80A fuse).

Given the additions, however I look at it and use diversity I need 80A.

Since I'll be inspected on this job (Mr NICEIC etc), I am sure this needs to be shown to be all ticked off OK. The quote from SSE is ÂŁ131.42+VAT to upgrade the fuse. Surely all they are likely to do is confirm Ze, check the supply cable and earthing conductor, and change the fuse. (modern cable and 16mm main earthing conductor).

Is this a typical quote? I haven't told the customer yet but he's not going to like it given that in his eyes he gets nothing for it.

Is someone here now going to tell me that they just change the fuse anyway without informing DNO? DNO never seem know what the fuse rating is anyhow when I've asked them before.

Justin

they have installed this BS1361 60A either because they didnt have an 80A on the van or they did it knowing more money again for company in years to come YOU CHANGE IT to 80A ÂŁ40 you say its got a modern supply cable same as any other.
"just put my tin hat on" :army:
and yeh DNO wont like it cause they havnt got there ÂŁ131.42 +vat
 
they have installed this BS1361 60A either because they didn't have an 80A on the van or they did it knowing more money again for company in years to come YOU CHANGE IT to 80A ÂŁ40 you say its got a modern supply cable same as any other.
"just put my tin hat on" :army:
and ye DNO wont like it cause they haven't got there ÂŁ131.42 +vat


There's a more than good chance that, that 60A BS1361 fuse has been sitting in that service head cut-out since the 50's or 60's, long before 80A fuses became the norm!!!

As for changing it yourself, ...well, your the same guy that liked the idea, that you can convert your service head to PME yourself!!! ...Enough said!!!
 
Last edited by a moderator:
As E54 has said, that fuse will probably have been there since the service was installed in the 50's, the service cable may well only be an 0.0225" service so don't get dropping a 100a in
 
Had similar issues as you the other day apart from it was a 7.5kW supply. Was told by the DNO system planner that everybody has a 'right' to a 15kW supply but their standard supply is 80A.
Two guys came out on Monday and altered the cutout position and meter positions, fitted a four pole isolator (econ 7), upgraded cutout to 80A and was told that the max charge would be around ÂŁ70 if they bothered to charge!
The DNO's do know what fuses are fitted and do know what the earthing systems employed are at individual properties. They will come out a couple of times to change the cutout fuse free of charge before they suggest you apply for a supply upgrade.
Personally I think the dangers of peeing off the local DNO boys by unauthorised alterations far outweighs the benefits gained from keeping them sweet
 
Had similar issues as you the other day apart from it was a 7.5kW supply. Was told by the DNO system planner that everybody has a 'right' to a 15kW supply but their standard supply is 80A.
Two guys came out on Monday and altered the cutout position and meter positions, fitted a four pole isolator (econ 7), upgraded cutout to 80A and was told that the max charge would be around ÂŁ70 if they bothered to charge!
The DNO's do know what fuses are fitted and do know what the earthing systems employed are at individual properties. They will come out a couple of times to change the cutout fuse free of charge before they suggest you apply for a supply upgrade.
Personally I think the dangers of peeing off the local DNO boys by unauthorised alterations far outweighs the benefits gained from keeping them sweet

Which DNO was that?
 
I just spoke to SSE DNO.

Up till April they charged nothing for this.

Since April thay are charging ÂŁ131.42 + VAT. Apparently they change the cut-out also and this with two blokes and call out and 1.5 hours is where they get the cost.

Shame I didn't do it three weeks ago.
 

Reply to Supply fuse - quote to change. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
745

Similar threads

  • Question
There's a church in a town near me that has solved the heating problem for most days by building what is essentially a large timber and glass...
2
Replies
27
Views
2K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top