Hi guys,
I'm going to put a cabin on my garden which is going to be made into a hair salon.
im starting to confuse myself on how to run the supply in to the cabin.
current arrangement in house is a dual RCD consumer unit (plastic)
TNCS supply.
in the cabin there will need to be power for maybe 3 lights
3 heaters at probably around 2000w each
a water boiler supply
and probably a radial circuit for general power

i was was thinking to run a 10mm 2 core armoured supply terminating it into adapt box and running a 10mm T&E to the consumer unit
part of it will be buried
now I know I shouldn't be exporting the PME and should put the cabin on its own TT system
im just curious on best way to connect this back up at the house avoiding discrimination of RCDs
there will also be extraneous parts within the cabin ie water supply (would any bonding be required even though it's bonded within the house) probably a silly question.
i appreciate your thoughts but it's something I have not come across before.
any thing else you need to know just ask.
 
10mm cable on a 40A breaker should be fine for the loading you require.
Unfortunately, you WILL HAVE to TT your cabin as it has a mains water supply that will require a main protective bonding conductor from the TT supply. This is because it could introduce separate earth potential and if there is a fault on the supply neutral, all of your water heaters, taps etc would become live at mains voltage, giving your customers the hair style they would not want!
As for the discrimination, up to you! If I was quoting this job I would give you the two options of either that way. Or taking a new supply from the mains to a new C.U in the building. OBV not on 10mm tho .
 
10mm cable on a 40A breaker should be fine for the loading you require.
Unfortunately, you WILL HAVE to TT your cabin as it has a mains water supply that will require a main protective bonding conductor from the TT supply. This is because it could introduce separate earth potential and if there is a fault on the supply neutral, all of your water heaters, taps etc would become live at mains voltage, giving your customers the hair style they would not want!
As for the discrimination, up to you! If I was quoting this job I would give you the two options of either that way. Or taking a new supply from the mains to a new C.U in the building. OBV not on 10mm tho ��.

That is an option, not necessarally the only one though, the house has a perfectly good earthing system, why would you side step it for a less reliable method?

@The OP - you are not allowed to extend your PME system, I think you meant extend your equipotential zone which you are allowed to do, 2 very different things in deed :)
 
Last edited by a moderator:
10mm cable on a 40A breaker should be fine for the loading you require.
Unfortunately, you WILL HAVE to TT your cabin as it has a mains water supply that will require a main protective bonding conductor from the TT supply. This is because it could introduce separate earth potential and if there is a fault on the supply neutral, all of your water heaters, taps etc would become live at mains voltage, giving your customers the hair style they would not want!
As for the discrimination, up to you! If I was quoting this job I would give you the two options of either that way. Or taking a new supply from the mains to a new C.U in the building. OBV not on 10mm tho .

10mm might not be fine depending on installation method and length of run. Also the water main could be plastic and therefore wouldn't need bonding.
 
10mm cable on a 40A breaker should be fine for the loading you require.
Unfortunately, you WILL HAVE to TT your cabin as it has a mains water supply that will require a main protective bonding conductor from the TT supply. This is because it could introduce separate earth potential and if there is a fault on the supply neutral, all of your water heaters, taps etc would become live at mains voltage, giving your customers the hair style they would not want!
As for the discrimination, up to you! If I was quoting this job I would give you the two options of either that way. Or taking a new supply from the mains to a new C.U in the building. OBV not on 10mm tho ��.

do you have a crystal ball? How do you know the length of run.
A
 
10mm might not be fine depending on installation method and length of run. Also the water main could be plastic and therefore wouldn't need bonding.

Installation method is clipped direct and buried for about 5 metres, total run is about 10metres.
The water supply will be in copper so i will have to bond the water. TT apears to be the way then?
 
Ok fair enough. I would personally put it on a TT if it has extraneous conductive parts though.And yeah I agree, volt drop, length of run and installation method of cable should be taken into account of course. Guess I just assumed it was a small garden size
 
Hi guys,
I'm going to put a cabin on my garden which is going to be made into a hair salon.
im starting to confuse myself on how to run the supply in to the cabin.
current arrangement in house is a dual RCD consumer unit (plastic)
TNCS supply.
in the cabin there will need to be power for maybe 3 lights
3 heaters at probably around 2000w each
a water boiler supply
and probably a radial circuit for general power

i was was thinking to run a 10mm 2 core armoured supply terminating it into adapt box and running a 10mm T&E to the consumer unit
part of it will be buried
now I know I shouldn't be exporting the PME and should put the cabin on its own TT system
im just curious on best way to connect this back up at the house avoiding discrimination of RCDs
there will also be extraneous parts within the cabin ie water supply (would any bonding be required even though it's bonded within the house) probably a silly question.
i appreciate your thoughts but it's something I have not come across before.
any thing else you need to know just ask.

Why add unnecessary connections?
 

Reply to Supply to cabin in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

Similar threads

  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K
  • Question
No, that is part of a different earthing system, don't mix the different earthing systems unless you have given proper engineering consideration...
2
Replies
27
Views
3K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top