I've inherited a mess that needs sorting. It's a supply to a garage. At the moment it looks like this:
Company Fuse into house is 60 A
Tails to CU are 16mm
Earthing is TN-S
Supply comes into the house on the ground floor by the the front door.
To get the supply to the garage, somebody has put 10mm T+E cable into the consumer unit with a 32A MCB
This cable goes into the roof space, is laid unsecured on the rafters and runs to the back of the house.
The cable exits the house by being shoved through a gap in the eaves, drops into the back garden, runs in small bore drainage bike to the bottom of the garden, under a narrow lane (buried to 50cm) and then into an ancient 4 way consumer unit in the garage.
It looks lethal. I've disconnected it.
This is what I propose to do:
All comments and suggestions gratefully received.
Thanks.
Jim
Company Fuse into house is 60 A
Tails to CU are 16mm
Earthing is TN-S
Supply comes into the house on the ground floor by the the front door.
To get the supply to the garage, somebody has put 10mm T+E cable into the consumer unit with a 32A MCB
This cable goes into the roof space, is laid unsecured on the rafters and runs to the back of the house.
The cable exits the house by being shoved through a gap in the eaves, drops into the back garden, runs in small bore drainage bike to the bottom of the garden, under a narrow lane (buried to 50cm) and then into an ancient 4 way consumer unit in the garage.
It looks lethal. I've disconnected it.
This is what I propose to do:
- Ask the DNO to upgrade the company fuse to 100A, upgrading the supply cable if necessary
- Fit an 80A switch fuse
- Connect this to the supply using 16mm tails
- Run 16mm swa three core cable from the switch fuse as per the existing route but support it every 600mm with cleats and raise it off the floor in the roof space so that it is attached to the brickwork.
- Clip the cable with cleats every 600mmin a clearly visible position to the robust fence which runs the length of the garden.
- Take it under the lane at a depth of 1m
- Take in into a new CU at the garage end
- Earth at either end using the earth conductor.
- Replace all the cabling and accessories in the garage on the basis that if the feed out there is that bad, then the rest is going to be quite poor too.
All comments and suggestions gratefully received.
Thanks.
Jim