supply to log cabin
W
webby_58
hello all
i have to get a supply to a log cabin and have the following arrangment :
TN-S supply in house
House CU MCB's no RCD
supply to garage CU via 16amp MCB (2.5 t/e) / garage CU has 63a 30ma RCD
approx 35mtr to garage and 50mtr to house in cabin approx 6 sockets maybe an electric heater and 1 light circuit
i propose to spilt the tails in the house into 100a henley block and take a new swa to the cabin. CU in cabin with 30ma RCD 6a MCB for lights 16a MCB for socket ring
my query is the cable size. do i have to use 10mm swa 3 core to provide the correct size earth ?
what would be the best way to do this also taking into account cost.
please help.......!!!!
thanks in advance guys.
Cant believe this has come up again......no matter how many times we go over it there is always one who will pop out of the woodwork and insist an outbuilding must be separated.
But as Hawk points out,they never seem to be able to quote the regulations applicable.
just to throw a spanner in the works here.
If the summerhouse contained a hottub with extraneous parts ect, would there be a danger that there would be a potential difference between the ground that awet person may step on, and the earth from the TNS system that you have in the installation?
This in theory could cause a shock to somebody whp's resistance would be very low due to being wet.
In this circumstance, can you supplement the TNS earth with a rod, in order to bring the TNS earth to the same potential as the ground around your installation?
Ill be very interested to hear your replies
John
Absolutely.
In most cases of hot tub installs, the hot tub manufacturer will insist you install an additional earth rod adjacent to the hot tub in addition to an exported earth (if any) for this very reason.
OK could not find the reg!!!
The problem is the potential (arrgh) of touching two different grounds.
In the event of a L-E fault current will flow down the ground rod and the ground voltage will rise due to the ground resistance, often this voltage can get rather high before the protective device opens. If you happen to be in contact with the 'live' ground and a 'real' ground at the same time things can get bad
This is the reason for equipotential bonding, to ensure all grounded metalwork is at the same potential (they're connected together).
So long as all earth stakes that serve a particular building are connected to a single main earth terminal (MET) there is no danger, it's common to use multiple earth pits in commercial buildings in order to get the ground resistance down to acceptable levels, they're all linked to a single MET.
In your outbuilding it's actually safer to have a local ground, if you do export the house ground and there's a fault any metalwork connected to the ground terminal will rise towards L potential, if there's a water pipe in the outbuilding it will remain at 'real' ground, ouch if you touch both. This is the reason that exporting PME earth is prohibited in certain circumstances.
IMO I will install an rod, with rcd
If the requirements for main protective bonding are carried out within the outbuilding, how can 'any metalwork connected to the ground terminal' become live?
The OP is discussing a TN-S earthing system with far less stringent requirements for protective bonding conductor sizing so even the economic argument doesn't work on this scenario.
Guidance Note 8 has all you need to know on exporting earths, Figure 5.15 has particular relevance to this thread.
HASNT anyone else seen this line?
no mention of protection just split tails into henley blocks??
This statement confuses me slightly as surely if there were any extraneous conductive parts within the summerhouse then these would be bonded to the EMT also????
Exactly what I was trying to point out in post 36 that's the whole principal of an equipotential zone.
You will need to fit a swich fuse or similar to protect the SWA after the henly blocks.
From post 2 mate
