Hi Fellas
Sure i had another login but seems my account has been recycled......anyway.
Im running a supply to multiple portacabins and shipping containers.
The Supply is a TNS and is approximately 95m away.
I have decided on a 63A 3phase circuit and calculated the cable size @ that length to be 25mm (total volt drop at this distance is 11.5v (Calculated)).
It will be supplying a new DB which will be enclosed in an Ip rated enclosure and separate circuits to be supplied to each of the units/containers.
Ok so now my question, i have been reading the regs and guidance notes regarding this and it clearly says no PME which i completely understand, But what about a TNS supply?
I get that there can be a difference in potential between the earth supplied and the true earth but if theres an Earth rod for each unit.
I personally cannot see why this is not acceptable but please let me know what you guys think in this situation.
cheers
Darren
Sure i had another login but seems my account has been recycled......anyway.
Im running a supply to multiple portacabins and shipping containers.
The Supply is a TNS and is approximately 95m away.
I have decided on a 63A 3phase circuit and calculated the cable size @ that length to be 25mm (total volt drop at this distance is 11.5v (Calculated)).
It will be supplying a new DB which will be enclosed in an Ip rated enclosure and separate circuits to be supplied to each of the units/containers.
Ok so now my question, i have been reading the regs and guidance notes regarding this and it clearly says no PME which i completely understand, But what about a TNS supply?
I get that there can be a difference in potential between the earth supplied and the true earth but if theres an Earth rod for each unit.
I personally cannot see why this is not acceptable but please let me know what you guys think in this situation.
cheers
Darren