Hi Fellas

Sure i had another login but seems my account has been recycled......anyway.

Im running a supply to multiple portacabins and shipping containers.

The Supply is a TNS and is approximately 95m away.
I have decided on a 63A 3phase circuit and calculated the cable size @ that length to be 25mm (total volt drop at this distance is 11.5v (Calculated)).

It will be supplying a new DB which will be enclosed in an Ip rated enclosure and separate circuits to be supplied to each of the units/containers.

Ok so now my question, i have been reading the regs and guidance notes regarding this and it clearly says no PME which i completely understand, But what about a TNS supply?

I get that there can be a difference in potential between the earth supplied and the true earth but if theres an Earth rod for each unit.

I personally cannot see why this is not acceptable but please let me know what you guys think in this situation.

cheers

Darren
 
You might want to recheck with regards to volt drop as well. 11.5 just on the distribution circuit means all the circuits off the connect DBs will be below the required minimum especially the lighting.
 
TN-S is fine. the reason PME is frowned on is that a loss of the supply N ( and hence the site earth) would lead to the metal structures possibly becoming "live".
 

Reply to Supply to Portable buildings and portacabin/container in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
389
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
958

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top