Hi, after a bit of advice, i need to install a supply to a shed at the far end of a garden. There is to be a small consumer unit in the shed, feeding a couple of sockets and a 2 lights. The existing system is PME and the existing fuseboard has an upfront 30ma rcd, (use to be TT a few years ago). So the way i was thinking of doing it was to split the tails & install a small consumer unit next to the existing one a with a main switch and a 20a breaker to feed the circuit, pvc conduit up the side of the building into an adaptable box then SWA to the fuseboard in the shed. The fuseboard in the shed will have an upfront 30ma rcd & couple of breakers.

Anyone think of a better way or does this sound o.k

Cheers
 
No i am splitting before rcd, the customer wants a new consumer in the shed. I would normally take a supply from an existing unprotected fuse, but there isn't one. Also i dont need to protect the cable with an rcd going to the new fusebox on a TN system.
 
No calcs done yet. I am just looking at the most cost effective option didn't really want to have a consumer in the house as well as the one in the garage. I have spoken to a couple of sparks today who said i must rcd the supply to the shed. I said i would if it was tt, but buried or surface mounted on TN doesn't need it.
 
No calcs done yet. I am just looking at the most cost effective option didn't really want to have a consumer in the house as well as the one in the garage. I have spoken to a couple of sparks today who said i must rcd the supply to the shed. I said i would if it was tt, but buried or surface mounted on TN doesn't need it.

Why don't you rcd protect anyway? Put the rcd board in the house and non rcd board in the shed, then everything is rcd protected?
 
No calcs done yet. I am just looking at the most cost effective option didn't really want to have a consumer in the house as well as the one in the garage. I have spoken to a couple of sparks today who said i must rcd the supply to the shed. I said i would if it was tt, but buried or surface mounted on TN doesn't need it.
so did these electricians not understand the use of armoured subs to outbuildings on a TN?
 
The customer has specified that he doesn't want to go into the house to reset the rcd, if a lamp expires in the shed and trips the rcd. I dont think it is neccessary when using surface mounted conduit or surface or buried SWA on a TN system.
 
Ive lost count with the amount of times I have said this but will say it once again, splitting the tails would mean you would need to install a isolator as you need a main switch to isolate all supplies, I know no-one does it, well I do, haha but thought I'd mention it again.
 
[/QUOTE]because you dont want to be traipsing into the house to reset the damn thing whenever it lets go....
gardening maybe?...muddy boots perhaps?...[/QUOTE]

Good point Glenn! I'll just go back to my corner haha!
 
because you dont want to be traipsing into the house to reset the damn thing whenever it lets go....
gardening maybe?...muddy boots perhaps?...[/QUOTE]

Good point Glenn! I'll just go back to my corner haha![/QUOTE]na....join in fella...
take no notice of me.....
i like being crabby....
 
no if you have 2 consumer units bud you need one isolator to be there for both, not sure of the reg at the moment, I have put my BGB back in the van, but now you have asked I will try to look tommorrow if I get time.
 
You have the advantage over me as my book is in the van, however I'm fairly certain all electrical circuits need to be isolated at one source, I will have a good look tommorrow and post either way.
 
TBH, i can't find a reg. for that. looking at 537.1.4 it does not specifically stipulate a single isolator.

Quite right Tel My apologies, on this rare occassion I'm wrong :smilewinkgrin:
or perhaps a reg that was there once is no longer, that reg you stated could be looked at in different ways, however regardless of that I found a reg stating if there are mulipull supplies or more than one if you like a labell must be installed at source, so bearing this reg in mind it must be fine to do what the OP suggested, therefore bag on head time :13:
 

Reply to Supply to Shed in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
532
  • Question
It’s all a bit confused as he originally says I read that as with supply removed he was picking up 230v. My concern is/was that as the house...
Replies
13
Views
3K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
1K
  • Question
The original post could be clearer, but I believe you're essentially asking if the use of a lower rated rcbo would prevent tripping of an upstream...
Replies
5
Views
2K
nicebutdim
N
  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
626

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks