Smells like at least a 120mm SWA to me, possible 150mm.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Supplying electric 400 metres away in the Commercial Electrical Advice area at ElectriciansForums.net
The alternative is a journey of up to 30 minutes to get between the two headlands.
but this is based on a few assumptions.
The buildings are sort of offices used for monitoring purposes.
The load has been calculates at 58A which is why we are looking at 63A supply. Thanks for your idea of the extra core for the earth but would the earth potential voltage be a lot different between the meter buildings and the proposed new buildings? There is just under 400m of made up land using rocks to gain the height. Probably 300m is a sea wall.
It is an unusual project - almost unique - as I do not think that using concrete which would be on a rock formation would be suitable. The rock under the concrete would dry out in dry weather thus reducing the efficiency of the earthing.
Any constructive suggestions welcome.
Also, as this is for a charity, is anyone interested in it?
Maybe a challenge for a college..............
That is why it is crucial to have specs for something like this Lenny, I can't for the life of me see an office building having a total load of 58amps, unless it was a 3 story office block.
I don't think I would suggest a single phase supply with a 60amp load over 400mts, it is just not economical it would have to go to 3 phases