Surge protection cable length | on ElectriciansForums
Discuss Surge protection cable length in the UK Electrical Forum area at ElectriciansForums.net
Stirling
Hi all
question regarding the length of surge protector cables. I have read the reg 534.4.8 that states that the length should not exceed 500mm. Is that for each conductor so every conductor should be 500mm or less. So with a 3 phase surge protector all 3 phases/neutral and earth should not exceed 500mm is that correct ? Thanks in advance ?
This could be pretty much impossible to be able to install a SPD on a three phase board external as some consumer units have there earth bars at the top of the boards so defo exceeding 500mm. Could be well over a meter ?
The Length can be reduced by simply bolting the PE to the earthed chassis of say the DB enclosure, rather than using a separate conductor and adding to the length.
See Hager’s version
  • [ElectriciansForums.net] Surge protection cable length
Oh right yeah, they look decent no cable connections either. So to clarify on a three phase consumer unit. It’s the length of the any phase conductor and earth conductor combined that can’t be over 500mm ?
Yes pretty much, it can exceed 0.5 meters but not 1meter.
Reply to Surge protection cable length in the UK Electrical Forum area at ElectriciansForums.net
From the title and first post it is not clear whether you are looking to install surge protection or a lightning protection system (LPS) or is it...
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...