Surge Protection Device on old installations | on ElectriciansForums

Discuss Surge Protection Device on old installations in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

punkin

-
Joined
Nov 19, 2012
Messages
30
Reaction score
9
Location
sheffield
Hi
I always thought installations were safe at the time of instalment etc, the Distribution Boards at my works were installed over ten years back.

Our company just had its EICR done. The tester gave us a C2 for a number of DB’s which don’t have Surge Protection Device installed, these DBs with the C2 do have lighting and emergency lighting circuits.
Do we have to have these SPD’s installed now because of 18th edition amendment 2 or should it be a C3 for a recommended device in the DB’s for old boards.

Many thanks.
 
C1 – There is a danger present, risk of injury and immediate remedial action required.
C2 – There is a potential danger present and urgent remedial work is required.
C3 – Improvement is recommended.

how can anyone justify a surge protection issue as a potential danger?
 
I presume that the reasoning is that there are life safety systems present (i.e. the emergency lighting installations). That said I would probably personally consider the classification of the Observation to be rather harsh.
 
C1 – There is a danger present, risk of injury and immediate remedial action required.
C2 – There is a potential danger present and urgent remedial work is required.
C3 – Improvement is recommended.

how can anyone justify a surge protection issue as a potential danger?
Exactly, having no SPD isn't a potential danger with urgent remedial work required.
 
I presume that the reasoning is that there are life safety systems present (i.e. the emergency lighting installations). That said I would probably personally consider the classification of the Observation to be rather harsh.
I agree, its defiantly harsh to put it as a C3
 

Reply to Surge Protection Device on old installations in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
980
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It is not a brand that I know, but on the appearance it would look like a good enough choice for most situations where you do not expect a direct...
Replies
7
Views
956
  • Question
You need a CT clamp at main tails, it depends on the rules where you are - you used to be allowed wireliss ones (such as MyEnergi Harvi), these...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top