MCS standards require that you comply with the PV Installation Guide -
http://www.electriciansforums.net/photovoltaic-solar-panels-green-energy-forum/23511-pv-guide.html
This says -
2.2.4.1 Lightning Protection Systems
Where there is a perceived increase in risk of direct strike as a consequence
of the installation of the PV system, specialists in lightning protection
should be consulted with a view to installing a separate lightning
protection system in accordance with BS 6651.
Note: It is generally accepted that the installation of a typical roof-mounted
PV system presents a very small increased risk of a direct lightning strike.
However, this may not necessarily be the case where the PV system
is particularly large, where the PV system is installed on the top of a tall
building, where the PV system becomes the tallest structure in the vicinity,
or where the PV system is installed in an open area such as a field.
If the building or dwelling is fitted with a lightning protection system
(LPS), a lightning protection installer should be consulted as to whether, in
this particular case, the array frame should be connected to the LPS, and
what size conductor should be used.
Note: In some cases it may be possible to forgo bonding to the LPS if the array
frame is sufficiently far away from it. A system for determining whether
it is necessary can be found in BS 6651 – ‘Code of Practice for Protection of
Structures against Lightning’. Alternatively, consult the installers of the LPS.
Where an LPS is fitted, PV system components should be mounted away
from lightning rods and down leads ( see BS 6651). For example, an
inverter should not be mounted on an inside wall that has a down lead
running just the other side of the brickwork on the outside of the building.
and
2.2.4.2 Surge Protection measures
All d.c. cables should be installed to provide as short runs as possible, and
positive and negative cables of the same string or main d.c. supply should
be bundled together, avoiding the creation of loops in the system.
This requirement for short runs and bundling includes any associated
earth/bonding conductors.
Long cables (eg PV main d.c. cables over about 50 m) should be installed
in earthed metal conduit or trunking, or be screened cables such as mineral
insulated or armoured.
Note: These measures will act to both shield the cables from inductive surges and,
by increasing inductance, attenuate surge transmission. Be aware of the need
to allow any water or condensation that may accumulate in the conduit or
trunking to escape through properly designed and installed vents.
Most grid connect inverters have some form of in-built surge suppression,
however discrete devices may also be specified.
Note: To protect the a.c. system, surge suppression devices may be fitted at the
main incoming point of a.c. supply (at the consumer’s cut-out).
To protect the d.c. system, surge suppression devices can be fitted at the
inverter end of the d.c. cabling and at the array.
To protect specific equipment, surge suppression devices may be fitted
as close as is practical to the device.