i have 1 of these to wire up this week and im not to sure how these are wired up

basically its a home office with dado trunking with 20 single sockets these will be made into the ring and at the end of the trunking will be the surge protection and breaker in an enclosure

any advice will be helpfull
 
Hey mate

I found this.

Installation and connection
The main protection SPDs are
installed directly after the main
incoming switch or RCCB
(type S).
SPDs can be used in any supply
system e.g TNCS, TNS, TT.
Options: Replacement
cartridges.
Connected in parallel to the
equipment to be protected.
Protection is assured in both
common and differential modes.



Also If you look at page 66 of the PDF you will find all the wiring diagrams for them.

Hope this helps.





you my friend are god

iv found the diagrams and it makes a bit more sense now
 
SPD's normally fitted upstream of rcds afaik (unless rcd is time delayed )-to prevent nuisance tripping - and wired in parallel with loads to divert surges(via earth)

the high-integrity earthing is for 'standing leakage 'over 10mA afaik =it will prob prevent a dangerous touch voltage if a screw works loose etc


it's not to handle leakage as such-it's to ensure the integrity of the circuit cpc
 
Last edited by a moderator:

Reply to the thread, titled "surge protection" which is posted in Australia on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top