Is it a requirement of 17th edition to run a seperate
Cpc with a 4core 3phase supply ? ?
Cpc with a 4core 3phase supply ? ?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss swa and seperate cpc problem in the UK Electrical Forum area at ElectriciansForums.net
all 4 cores up to 95mm² are fine to use armourings as cpc.
No .Is it a requirement of 17th edition to run a seperate
Cpc with a 4core 3phase supply ? ?
Hi engine 54, can u offer some evidence to support this?
have a read of 543, plenty of useful info in that area of the BGBas far as i can see the CSA of SWA armourings upto 95mm² is larger than the associated line conductor so how can it not be suitable?
I would just take his word for it ;-)
as far as i can see the CSA of SWA armourings upto 95mm² is larger than the associated line conductor so how can it not be suitable?
Pep your right if you use 90 degree at 70 degree current carrying capacity levels!
90D at 70D is good up to240mm
90D at 90D fails at 16mm, 95mm and all above 150mm including 150mm.
THE ABOVE IS 4CORE - Table D10a and b refer of GN1 (Appendix B of GN 8 for more)