Hi engine 54, can u offer some evidence to support this?

the regs require , for the most part, that bonding conductors to be at least 10mm ,
but because swa has a resistivity roughly 8 times greater than copper , you would need the swa csa to be at least 80mm2 ( equivolent to 10mm copper ) if that cable were to be used for bonding purposes.
which makes some of the smaller cable swa's acceptable as cpc's but not for bonding.
basically speaking.
 
the regs require , for the most part, that bonding conductors to be at least 10mm ,
but because swa has a resistivity roughly 8 times greater than copper , you would need the swa csa to be at least 80mm2 ( equivolent to 10mm copper ) if that cable were to be used for bonding purposes.
which makes some of the smaller cable swa's acceptable as cpc's but not for bonding.
basically speaking.

And can become considerably more involved when meeting bonding requirements On larger PME and on larger commercial and industrial installations. Many of which the typical domestic 10mm bonding conductors won't come close to complying!! In such cases, a separate full sized conductor is generally the only means of complying, when installing a 4 core (3 ph + N) cable...
 

Reply to swa and seperate cpc problem in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
281
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
270
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
351

Similar threads

totally agree
Replies
12
Views
1K
  • Question
It's the same with any system, if you put poo in, you get poo out!
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top