Hi guys,

I am running a supply to an outbuilding that requires a 22m run from the Main CU (in the garage) to the CU in the outbuilding, at the Main CU it will be a 40A MCB supplying an 63ma RCD protected sub board which will then supply:

6A type B MCB for 12 downlights and an extractor fan
32A type B MCB for 3 double sockets
20A type B MCB for a 3.5kw split air condition unit

I've calculated the voltage drop if using 6mm 3 core SWA clipped direct (table 4E4A p372 BS 7671) 53 x 40A x 22m / 1000 = 46.64 Vdrop .. thats a crazy figure

And the supply will be feeding a sub board initially based on what I've been taught I calculated maximum demand by adding the breakers amp size and x them by 40% so 6+32+20 x 40% = 23.2A

The SWA will run up the outside wall from the garage into the loft and out the other end, and down galvanised conduit, into the ground and into and up a wall with insulation (2m) and into the outbuilding

The queries I have are:

The majority of the run will be clipped direct and only a small part of the length will be in insulated brick wall am I right/wrong to assume Reference method C (clipped direct)?

And as it is SINGLE PHASE 3 CORE cable I'm using I'm a little confused as the only two options under clipped direct in table 4E4A (p372 BS 7671)is '3 CORE 3 phase AC' and '1 two core cable SINGLE PHASE AC' my installation does not fall perfectly into either option, which should I select?

And how best would you recommend lowering the Voltage drop to the stipulated 5% 11.5V?


Thank you in advance for helping,

Mark
 
Nobody has mentioned the reference method. Clipped direct has a higher ambient temperature than buried, which is usually lower as it's cooler below 500cm. So, go for the one which has the higher impact on the temperature of the cable, so at least choosing clipped direct was right. And I still don't know why you are thinking about running 10mm armoured in conduit. The steel armour inside is there to protect the conductors. Good luck getting armoured around a bend
 
Nobody has mentioned the reference method. Clipped direct has a higher ambient temperature than buried, which is usually lower as it's cooler below 500cm. So, go for the one which has the higher impact on the temperature of the cable, so at least choosing clipped direct was right. And I still don't know why you are thinking about running 10mm armoured in conduit. The steel armour inside is there to protect the conductors. Good luck getting armoured around a bend
Think the OP has already binned that idea
 
Hi all, Thank you for your feedback you were right I have scrapped the SWA in galv conduit idea.
Just a quick one would I be able to use 6mm SWA as the subboard distribution supply as I have spoken to another spark I know who thinks this would be adequate hence why originally thought that would do, and also I remeasured the run and its 30m of SWA not 22m as stated before.

Regards,

Mark
 
At 30m the volt drop would exceed the permitted maximum though..(going by the book)....though in practice we all know 6.0mm would be perfectly OK.
yeah, but OP has used 40A for his Ib. in practice 25 - 30A would be more realistic.
 
Seeing your nice pic has reminded me there is a run inside the house. If there's insulation involved that may add weight to the 10mm, or a bit more care to avoid it... Just saying :)

Another thought :

55mm x 55mm Cable Guard - 2Mtr Length - Black - https://www.tlc-direct.co.uk/Products/CG552BK.html?ad_position=1o4&source=adwords&ad_id=45425533757&placement=&kw=&network=g&matchtype=&ad_type=pla&product_id=CG552BK&product_partition_id=174053380627&test=finalurl_v2&gclid=EAIaIQobChMIz5emr6-u1QIViLvtCh355guSEAQYBCABEgLg7PD_BwE

[ElectriciansForums.net] SWA armour supply to outbuilding, what CSA cable? and Reference Method?
 
Last edited:

Reply to SWA armour supply to outbuilding, what CSA cable? and Reference Method? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
290
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
276
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
575
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
2
Replies
21
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top