At what size of SWA cable are you required to run an external earth ? I'm inspecting a distribution system and its a complete mess. No main earths anywhere but they have utilized the armour and are using at is their earth. I can't find anything in the regs book, is there possibly something in the guidance notes I can refer to ?
 
Hi Paul - if you've got GN8 its Appendix B. There's a few tables, this is just the first one. Hope that helps :)

[ElectriciansForums.net] SWA armouring as Earth
 
At what size of SWA cable are you required to run an external earth ? I'm inspecting a distribution system and its a complete mess. No main earths anywhere but they have utilized the armour and are using at is their earth. I can't find anything in the regs book, is there possibly something in the guidance notes I can refer to ?
SWA CPC.pdf
 

Attachments

  • SWA CPC.pdf
    991.5 KB · Views: 57
At what size of SWA cable are you required to run an external earth ? I'm inspecting a distribution system and its a complete mess. No main earths anywhere but they have utilized the armour and are using at is their earth. I can't find anything in the regs book, is there possibly something in the guidance notes I can refer to ?

There is no limit on size where a separate conductor is required, it depends on the individual conditions of the installation.
When assessing an existing installation the table 54.7 can be used as a first reference, but if this shows that the armour is inadequate you must then use the adiabatic equation as that may show that it is adequate.
Table 54.7 often gives a larger conductor size than is actually required.

You also need to consider whether the cpc also needs to perform the function of a bonding conductor, this usually changes things considerably.
 

Reply to SWA armouring as Earth in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
776

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
1K
  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
703

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top