Dear all
Testing a garage that is fed in 2 core swa using the swa as cpc
Live and neutral are 2.5mm. I know the swa is fine as a cpc but I’m unsure what size to put on certificate for it
Seen a table that says it’s equivalent to 17mm but in the back of my mind I remember you need to divide by 8.8
So which goes on the very. 17mm or 1.93mm
Thanks in advance
Cheets
 
You are correct in saying the csa is 17mm and the 8.8 factor (there are other factors within the same ball park) gives its conductivity in terms of copper. Most people will just note swa in the column as opposed to a csa.
 
You are correct in saying the csa is 17mm and the 8.8 factor (there are other factors within the same ball park) gives its conductivity in terms of copper. Most people will just note swa in the column as opposed to a csa.
Hi westward. Thanks for the reply( prompt as usual). I didn’t think I could put swa in the box of the cert. it’s the Niceic online cert and I think it needs a number so I guess I go with 1.9mm
 
Record the CSA in the box, it doesn’t ask for the ‘copper equivalent’ or calculated value, just the actual CSA.
If you had aluminium conductors would you calculate the ‘copper equivalent’ or just record the CSA?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
South coast

Thread Information

Title
Swa as cpc what size ?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9
Unsolved
--

Advert

Thread statistics

Created
dnjr,
Last reply from
davesparks,
Replies
9
Views
3,059

Advert

Back
Top