sorry if I'm dwelling on this but have to supply 230v to a hot tub on PME.
load 32amps.
separate RCD back at the house, 54 mtrs away.
exporting PME through third core and armoured sheath.
no extraneous conductive parts at the tub.
MCB 40amp type C ZS - 0.57ohms
Cable is going to be clipped direct all the way down.
after calculating volt drop and ZS the only one i can fit is 10mm three core. 6mm will do the V drop but not the Ze.
has anyone got one of these quick apps they can check this.
only asking as this is the first hot tub i have done at this distance.
thanks