A 4-core SWA cable laid to supply power to a garden room is not functioning - on doing a continuity check I have established that only 3 of the cores have end to end continuity but the fourth (yellow) reads as an open circuit.

Will this mean a new cable?
 
could be a sign that the cable has broken down and after a few months of service will finally die. might be an idea to IR all the core and armour, see if there's low insulation resistance. if it's just 1 core down, you still got 3 to play with.
 
It depends, do you need all 4 cores and is the outer sheath damaged at all, does the cable pass its Insulation tests as it could be a warning sign of a progressive problem, can you confirm is earthed up and give you a good ELI reading, lastly is there an rcd covering this cable?

Bugger tel' beat me again ... Hmmmph same advice though!

Tel'!!!! is that someone at yer door, maybe i can get a post in edgeways ;)
 
Last edited by a moderator:
A 4-core SWA cable laid to supply power to a garden room is not functioning - on doing a continuity check I have established that only 3 of the cores have end to end continuity but the fourth (yellow) reads as an open circuit.

Will this mean a new cable?

If you have conducted all the tests suggested above, and this yellow core is definitely broken then Yes, you will need to change this cable. You can bet your bottom dollar that the sheath has been compromised. Probably by a sharp stone or other sharp debris, going through the sheath and between the armouring strands on into the conductor(s), it will also mean the SWA will be corroding away. So eventually you won't have any CPC protecting this cable.

Easiest way to check this, is to disconnect this cables SWA glands at both ends from any earth contact and conduct a sheath test!! Achieving any reading on the test, will indicate the sheath has been compromised, and replacement will be required!!
 
b&q have your answer.....

[ElectriciansForums.net] SWA continuity
 
A 4-core SWA cable laid to supply power to a garden room is not functioning - on doing a continuity check I have established that only 3 of the cores have end to end continuity but the fourth (yellow) reads as an open circuit.

Will this mean a new cable?

Firstly, establish exactly what each core does, or not, and when it last worked if it ever did in the first place.

That should tell you when the gardener last visited, or not.

Secondly, establish whether or not there is continuity on each core and armour

Thirdly, establish whether there is a high IR between all the cores and armour when disconnected at each end.

If the cable has been damaged it is likely to show up pretty quickly.

I had this type of fault last year, 4-core 16mm2 supplying a garden office using only 3 cores with no armour bonding was repaired by a plumber who jack hammered through the cable when laying a water pipe. poorly jointed with a torpedo , then subsequently failed after a couple of years.
Found at least 4 joints in the run where the builder was attempting to be artistic. So I decided to run a new 6mm2 3 core cable.
 
Firstly, establish exactly what each core does, or not, and when it last worked if it ever did in the first place.

That should tell you when the gardener last visited, or not.

Secondly, establish whether or not there is continuity on each core and armour

Thirdly, establish whether there is a high IR between all the cores and armour when disconnected at each end.

If the cable has been damaged it is likely to show up pretty quickly.

I had this type of fault last year, 4-core 16mm2 supplying a garden office using only 3 cores with no armour bonding was repaired by a plumber who jack hammered through the cable when laying a water pipe. poorly jointed with a torpedo , then subsequently failed after a couple of years.
Found at least 4 joints in the run where the builder was attempting to be artistic. So I decided to run a new 6mm2 3 core cable.

If the sheath is proved damaged via a sheath test and a core is proven open circuit, then this cable is a dead duck in the water...lol!!!
 
Why is a 4 core being used?

Because thats all the spark could get out of his work lol

Anyway make sure you are testing this end to end ie no junction box under the floor also and sorry to bang on about this but more info required ie I take the 4 cores are red,yellow,blue and black plus what is the yellow being used for
 
If the sheath is proved damaged via a sheath test and a core is proven open circuit, then this cable is a dead duck in the water...lol!!!

You've got me there, what is a sheath test?

We are not talking Durex here are we ?

Let me see..... a 50V AC Ohmmeter generating 25A ?
 
Last edited:
A very simple test between the SWA and earth!! The earth can be via a test spike into the soil or any earthed metal work... Obviously any reading between the isolated SWA and earth will indicate that the PVC outer sheath has been compromised /damaged!! The simple test can be performed with a low ohm meter (my prevalence) or IR tester....
 
I think that would depend which end of the SWA is measured to earth, presumably, at the MET? If measured at the 'other end you would be measuring the resistance of the armour.

If the cable installation was likely to be costly, then you could consider a Murry Loop Test. which would then identify the position of the fault along the run.
 

Reply to SWA continuity in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
1K
  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
703

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top