I love these discussions - The sub main will only be feeding 3x cooker isolators which will be surface cabled and mounted. The isolators are 3 meters away from the metal sink unit & the nearest cooker outlet point would be about 1.5 metres from the sink unit. Probably not going to provide RCD protection on the cooker circuits.
If the pipes feeding the kitchen sinks have been bonded already, should there be any requirement to bond them to the sub main board???
The area that the sub main will be in is an internal room and no adverse conditions apply, the same applies to the board that it will be fed from.
Myself, I can't see any problems with using the armour of the swa and leaving the bonding as it is - but always happy to be proved wrong.
As a kitchen is not classed as a special location in the BS 7671-2008 then is there a need to have that sink bonded at all?
If your not geting a low enough Zs for disconnection times on an existing circuits protection device then yes a way to achieve a safe enviroment by limiting the touch voltage is by the use of supplementary equipotential bonding in the kitchen and the metal work, that is proved to be an extraneous conductive part, within it. Though as your installing new circuits there are better ways to achieve disconnection times, by installing conductors of a large enough CSA to obtain the low enough Zs or the use of an RCD, my prefered option is cable CSA. IMO supplementary equipotential bonding should be something that is only used in a special location, which a kitchen in not classed as.
Also you can check the effectivness of the bonding by making a test between the pipe work, extraneous conductive part, if it is an extraneous part, and an exposed conductive part, case work of cookers, check out section 415 and in particular reg 415.2.2 for this.
You may find that the original installation was done to the 16th edition or perhaps by a sparks use to the 15th where the attitude was metal pipe ..bond it .........must be safe!!
If it does need bonding, which to be honest I doubt, unless it was fitted to achieve safety on an existing circuit, then as it would be supplementary equipotential bonding, then it should be done exactly the same as you would in a location containing a bath or shower, and that is connecting the bonding conductor to the CPC within the location.