SWA current capacity. | Page 2 | on ElectriciansForums
Discuss SWA current capacity. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Where do you get 50% fom?
Table 52.2 (page 104 brb) :)
edit: from your description the SWA is running under a layer of insulation that is in excess of 100mm deep?
Why not run a wooden rail above the insulation and clip it to that.
ok so if i put 16mm onto cable tray above insulation current capacity goes up to 94a. would we all agree this is adequate?
more tah adequate. from a job i did last month, 10mm XLPE clipped direct is rated 81A so 16mm should fly it above insulation
Reply to SWA current capacity. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...