a query. If wiring to a sub, e.g. in a garage in SWA, using 1 core as earth, armour is earthed at supply end. My question is--- is there any reason not to also earth armour to the earth core at the sub end
 
Last edited:
agreed, just a belt and braces one. i use the SWA locking earth nuts, so no need for banjos, seems a pity to waste the nut's earthing facility
 
You not heard it whispered in dark corners that if a fault occurs and you connect both ends of a SWA you will create eddy's.

It's the same theorists that all bonding conductors should be kept tight as if there is a fault and 100's amps go down the condutor it can whiplash ...................

I must go to some wierd places
 
This type of thread has been going on for years personally i will allways gland both ends wether i insulate one end would be on the instructions of a qual.elect.engineer ,but it would be informative to get a definative answer from the IEE on where and what to do.

yours gb
 
Im not sure that eddy currents will flow in the event of a fault in a multicore armoured cable as the protection will clear the fault in such a short time that the eddy currents will not have time to establish and cause damage ie heating. Also if one core is being used a sthe earth then it is enclosed within the magnetic armour and will be cancelled out. I d know that single core cables with non magnetic sheaths should have the sheath bonded at one end only as during normal service eddy currents can flow and cause heating of the cable if both ends are bonded.
 

Reply to SWA Earthing in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
202
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
2K
I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top