if the bonding wasn't connected, then theres no connection to earth for the armour.

i'd say the armourd sheath is an extraneous conected part so needs to be connected back to the earth to allow the supply to be automaticaly disconnected by the circut protective devices should a fault occur.

would you not say that?
 
if the bonding wasn't connected, then theres no connection to earth for the armour.

i'd say the armourd sheath is an extraneous conected part so needs to be connected back to the earth to allow the supply to be automaticaly disconnected by the circut protective devices should a fault occur.

would you not say that?

No I wouldn't.
The SWA is connected to earth via the gland which would be connected to the steel casing of the DB board which is connected to the earth bar via the way it is made. Therefore you don't need a fly lead. If your DB casing is plastic than you would use a fly leadbut this would act as an extension of the earthed steel wire. Therefore an earth.
 
what steel casing on the DB, its not mentioned, did you presume it was steel, id tend to think if it was steel then the question wouldn't have been asked either way the reply is still the same supplementory bonding is 1/2 protective conductor 544.2
 
But it's not supplementary bonding.

Why can't you understand that?? The steel wire is not an extraneous part. For starters it's not part of a non-electrical condition because it's part of a cable!! Your not using the fly to bring it to the same potential your using it to earth the cable.

It's the same concept as having an earth wire in a bit of twin and earth. Can't get clearer than that.
 
so your latest presumption is the sheath is part of the cable,

now thats where i'm going wrong i'm saying the sheath is not part of the cable the cable is the cores the sheath is the armour protecting these cores, and with this being a metal part which will only become live under a fault condition will require supplementory bonding,

i was sure that bit of copper in T&E was the CPC and therefore part of the circuit.

are you now saying you presumed the sheath was being used as a CPC
 
no please 54 when i get proved wrong i have to correct it so it can only improve me.

i'd guess there are plenty of people out there who don't know these things so its an educational process, we have to stay current and if it turns out i am correct with my assumptions then that can't be a bad thing as it shows some of you old timers on these boards have to be prepared to back up your statements rather than confuse us all with general coments
 
Are you telling me that in all your time you have never used the STeel wire of SWA cable as a CPC?

I'm going to get my book out in the morning and quote all the regs back to you till it's coming out of your ears.
 
Archy its not trolling please feel free to jump in, but be aware whats tripping everyone up is termanology on this.

a question was asked i answered but the question is terminology is the connection to the armour on SWA earthing or bonding, because earthing doesn't exost according to the regs but bonding does and i beleive this bonding is supplementory or aditional
 
I reckon this thread was more industrial than house basher so as you said earlier " pblec " to Mark on another thread best you get back in your box !
 
Archy its not trolling please feel free to jump in, but be aware whats tripping everyone up is termanology on this.

a question was asked i answered but the question is terminology is the connection to the armour on SWA earthing or bonding, because earthing doesn't exost according to the regs but bonding does and i beleive this bonding is supplementory or aditional

It's your terminology that's mixed here mate.

So the term earthing don't exist? What is it called when you connect the CPC of a circuit to the earth bar than??
 
no please 54 when i get proved wrong i have to correct it so it can only improve me.

i'd guess there are plenty of people out there who don't know these things so its an educational process, we have to stay current and if it turns out i am correct with my assumptions then that can't be a bad thing as it shows some of you old timers on these boards have to be prepared to back up your statements rather than confuse us all with general coments

pblec,

After 28 years in the industry as an electrician, you shouldn't really be having this conversation, ...but You are!!!
 
i have used the outer core of swa as a cpc but that wasn't the question

i couldn't use it as CPC when i first qualified as the firm i worked for didn't allow it and even now i won't - but that doesn't mean its wrong.

i'm sorry but what it does mean is you need to get your head in a regs book and refresh your knowladge a little, its not an insult i've just opened my green book tonight because of these forums.
 
i have used the outer core of swa as a cpc but that wasn't the question

i couldn't use it as CPC when i first qualified as the firm i worked for didn't allow it and even now i won't - but that doesn't mean its wrong.

i'm sorry but what it does mean is you need to get your head in a regs book and refresh your knowladge a little, its not an insult i've just opened my green book tonight because of these forums.

Read on mate read on. Ive said nothing wrong in this thread and if you think I have prove it with a erg and why,

and you havnt answered my question, what is it called when a CPC is connected to an earth bar because the term earthing doesn't exist?
 
sorry mate i was trying to be diplomatic, i'm new on the forum and their has been a few mistakes made in this topic.

as you may know people read on forums and look at the number of posts then beleive everything they say, which is a bad thing.

just because i've been at it for 28 years doesn't mean i know everything, you will find i'll ask some bloody stupid questions that apprentices will know but it may be something i've just taken for granted
 

Reply to SWA Fly lead in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
564
loz2754
L
You are going to need something like this...
Replies
5
Views
384
  • Question
Ferrule kit and self-adjusting crimper in Lidl just now for £15 or so. What not to like? The colour tells you the ferrule size BUT there are two...
Replies
8
Views
566
  • Question
in the day of 2c cable we used the same size earth fly lead as the line cores never bothered to work it out
Replies
1
Views
2K
Thanks Brian. I'll keep doing it then, no harm I suppose. I am lucky in that being DIY, I have the luxury of time when it comes to this kind of...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks