There seems to be a tendancy now to wire single phase installations with 3 core SWA and ignore the armour as a conductore. What is the favoured way of installing 3 phase? 4 core T&N wth armour as earth, or 5 core TN&E? Indeed, is 35mm 5 core generally available?
 
Last edited:
Normally a 4core ,but if it was a long run you might have to run a seperate cpc so it might be an option to run a 5core if its in stock? also the cores might be white.So its down to calcs./spec./avai./& price

yours benji
 
I suppose if cost is important there is nothing wrong with using the armouring, as long as the locknuts are tight and don't corrode, work lose, ELI reads OK etc. Using 5 core eliminates this possibility so I would always go for 5 core, and have no problem getting hod of it.
 
I personally have never installed 5 core SWA and have only seen it once.

I can't see a problem in using the amour for a steel CPC and larger than 50mm cable running a seperated eath cable to reinforce the Ze

I think it comes down to personal choice,

I would say that if you base your costings for the more expensive option and the if the budget gets tight on the job, then you can change the spec for the cheaper option.

(this is assuming you haven't detailed the exact cable)

I think this is one for personal choice and there is no right or wrong answer

Richard
 
Thanks for all your answers. I think I'l use 4 core and check R1 vv R2 before going to the expence of running a seperate CPC.

Geoff
 
theres a reat page in GN1 that tells you if the SWA will be suitable for a CPC cant remember the page if i remmember correctly above 35mm 4c a seperate cpc has to be run and also some 16mm. double check first.
as for usinf a 5c remember the cpc can be smaller than live conductors so a seperate cpc will be cheeper.
 
Last edited:
If the installation is TN-S it would be prudent to lay a CPC of the same cross-sectional area as the conductors in a 4-core SWA cable in addition to securely bonding the wire armouring.
 
I've checked GN1 and it makes it quite clear that 35mm SWA has not just a little bit more than the required CU equivelent armour, but much more than adequate. Using 5 core or an additional earth is therefore not a requirement.

Regards,
Geoff
 

Reply to SWA for 3 Phase Installation in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
688
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
652

Similar threads

Came across 3No 1ph heaters connected by 2xT&E cables from a 3phase supply on an installation whilst carrying out an EICR few years back...
Replies
9
Views
733
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top