OK. GN1 specifies that for 35mm SWA the armour is an acceptable CPC. But here comes the runt.
Irrespective of the Regs, (or is it in very strict adherence of the regs?) the MET must be at the supply head and the main bonding must run to the MET. It is unacceptable, and they will NOT provide a connection, if the bonding is to a Dis Board fed from a sub main.
Also, tails of more than 3 meters are Unacceptable. If the tails would be more than 3 meters then you have to install a single way DB (switch fuse or other) within 3 meters and take the sub main from that. More over, and contarary to the EDF web site which only requires an isolator, but only in some areas, it must contain fuses (or I suppose some other form of cutout) . The Reason... "so that they do not have to change their fuses if there is a fault with the sub main". ... Sounds rediculous to me because there is no discrimination, however that is their requirement before thay will connect a meter.