Cant you just do a loop test when everything is up and running and all extraneous metal earthed by 10mm back to the met in the dwelling

Already been stated by the O/P that there is No extraneous metalwork/services within the shed...
Therefore no requirement for any 10mm bonding conductors on this installation!!
But i would personally still install a 3 core cable as a CPC, and still use the earthed armouring too....lol!!
 
Im with E54 on this one.

If the spa is housed and an equipotential zone is created, then it no different to a hot tub in the house.So i would install it to "Section 701" .

If the hot tub is not housed and an equipotental zone can not be created then i would install to "Section 702". As for PME, i would either TT the installation at the supply end of the Distribution Circuit, or place an Electrode at the "MET" with a predetermined Ra which would limit the touch voltage on a broken pen and also reduce the possible sensation of an electric shock through the difference in the two "Earth Potentials".

Chris
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
SWA for shed **PME** EARTH?????????????
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
16

Advert

Thread statistics

Created
Andy Ellis,
Last reply from
Chr!s,
Replies
16
Views
11,714

Advert

TrueNAS JBOD Storage Server

Back
Top