Cant you just do a loop test when everything is up and running and all extraneous metal earthed by 10mm back to the met in the dwelling

Already been stated by the O/P that there is No extraneous metalwork/services within the shed...
Therefore no requirement for any 10mm bonding conductors on this installation!!
But i would personally still install a 3 core cable as a CPC, and still use the earthed armouring too....lol!!
 
Im with E54 on this one.

If the spa is housed and an equipotential zone is created, then it no different to a hot tub in the house.So i would install it to "Section 701" .

If the hot tub is not housed and an equipotental zone can not be created then i would install to "Section 702". As for PME, i would either TT the installation at the supply end of the Distribution Circuit, or place an Electrode at the "MET" with a predetermined Ra which would limit the touch voltage on a broken pen and also reduce the possible sensation of an electric shock through the difference in the two "Earth Potentials".

Chris
 

Reply to the thread, titled "SWA for shed **PME** EARTH?????????????" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top