stef

-
Joined
Apr 23, 2009
Messages
578
Reaction score
66
Location
Gosport
Is this correct: a SWA cable runs from a 3 phase transformer to a distribution board (TNS). The SWA must only
be connected to earth on the transformer side to earth and not on the DB side otherwise you'd get a
second earth loop. But what harm can that do? :confused:
 
connect both sides if you have used 4 core spare as earth also BAD Practice in prmanent instals but as the tranny will be moved and inadvertantly knocked by builders leading to probable loosening of the gland IMO put an earth clamp on the armour at either end and connect to earth as I say its viewed as bad practice but due to conditions Id recomed that
 
Uhm, I forgot to mention: it is a 500 KVA transformer (11KV to 415V) which was installed by some DNO
contractors. I found it a bit odd why they connected one end only and when I asked them they mentioned the
second earth loop but didn't know exactly why.
 
Hi benji,

they were using 3 single core SWA per phase, don't know what size. There is a neutral as well.
I really don't know why the SWA is only earthed on one side. The contractors didn't know either, except 'it is always done like this'
 
No, they used glands on the transformer side only, on the DB side they used insulated clamps, clamping the cables on the insulating PVC sheath to the frame, (in other words: insulated from earth) and they used a separate earth conductor from the transformer frame and star point to the DB frame. I don't know, it looks a bit strange to me. I googled up and down but couldn't find an explaination for this
Shame that I couldn't take a photo.
 
normally use single cores with aluminium armour glanded both ends into non-ferrous gland plate at one end, think it,s to stop circulating current being induced into armour .how big was the db

yours benji
 
Sorry this is a bit late.

Armoured transformer tails are unusual, normally double insulated un-armoured. The reason for glanding just one end is to stop the armour wires becoming a giant 1/1 CT. At full load your 500KVA transformer would have 666A flowing in the armours.

I once had a situation where 1000KVA transformer was installed and the contractor decided that the brass gland nuts we’d provided were to nice to use so substituted steel, it was in a bolted terminal box so who would know. Things were OK for a while but as the load on the transformer grew so did the heat. I’m just glad I wasn’t around when the insulation finally melted in the transformer terminal box :eek:

The contracting company wasn’t around for long after that!
 
so if 1 end of the AWA is glanded into the ali gland plate, what happens at the other end? is it glanded into one of them insulating bushes, which is then glanded into the gland plate? in was on a power station and they all used AWA singles for their trannys, but i only glanded one end, and we were told by the engineer to just use ali glands straight into gland plate.

cheers mate!
 
I was referring to steel wire armour, aluminium can’t set up eddy currents, which cause the problems. The gland plates must have been aluminium, or steel with a slot between each hole. The slot is usually filled with epoxy resin before the plate is sprayed.
Earthing both ends of the tail armouring also causes problems with the restricted earth fault protection relays used on the LV side of a transformer.
 
Last edited by a moderator:
im a numpty, if course you cant induct into a non ferrous metal. hence te AWA. I wasnt aware that you can get SWA singles for the reason you mentioned.


Neither was I, all the transformers I’ve worked on had either double insulated or lead sheathed tails. Aluminium never crossed my mind! :mad:


The thread started with SWA armoured singles!
 
Neither was I, all the transformers I’ve worked on had either double insulated or lead sheathed tails. Aluminium never crossed my mind! :mad:


The thread started with SWA armoured singles!


are there any issues with earthing both ends of swa in general

when does this become a consideration?
 
Sorry this is a bit late.

Armoured transformer tails are unusual, normally double insulated un-armoured. The reason for glanding just one end is to stop the armour wires becoming a giant 1/1 CT. At full load your 500KVA transformer would have 666A flowing in the armours.

I once had a situation where 1000KVA transformer was installed and the contractor decided that the brass gland nuts we’d provided were to nice to use so substituted steel, it was in a bolted terminal box so who would know. Things were OK for a while but as the load on the transformer grew so did the heat. I’m just glad I wasn’t around when the insulation finally melted in the transformer terminal box :eek:

The contracting company wasn’t around for long after that!


still don't quite get this- are eddys currents an issue on swa's generally

SP and 3P if 'banjoed and flylead' both ends

ie: cpc and armour paralleled


or is it just singles ?
thanks for any info
 
With aluminium armouring or lead sheathing one end only will be earthed to stop circulating currents. I went back through my old apprentice training books to find out why we didn’t use aluminium armouring, all the plants produced or processed lime. Aluminium and lime isn’t a good mix, the lime rots the aluminium away, and for the same reason aluminium ladders weren’t allowed. Lead has to be plumbed to terminate it so the cores can be sealed with compound. Each plumbing cone at one end would be insulated from the terminal box. From what I’ve found out aluminium can be glanded at each end but one end like the lead must be insulated. On all the systems using lead the transformer end would be earthed while the switchgear end would be insulated.
Some of the transformers were installed with aluminium conductors but the terminations had to be protected from the lime with a horrible spray on yellow gunk that for the life of me I can’t remember what it was called.
My comment about eddy currents referred to an episode where a contractor used steel locknuts on double insulated singles instead of the brass he was supplied with. The gland plate was steel but with slots and the glands brass to stop the eddy currents, he f*^ked it up by pocketing the brass locknuts.
 

Reply to SWA from transformer to DB in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

You would treat it as a TT installation.
2
Replies
29
Views
1K
Sounds more positive.
Replies
8
Views
474
I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
564
Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
536

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks