Hi, looking for some advice,
6mm swa allready installed to a hot tub
Client now wants additions and my calcs say the original swa is allready too small.
26a but its120m run, im advising 16mm 2core.

However the swa installed is 4 core so was thinking of doubling cores together to save on time/ costs and putting rod in.

Any thoughts or potential issues with this?
 
My calculations also indicate 16 mm² for the hot tub alone. Doubling up using the other 2 cores of the 4 core would result in the equivalent of 12mm² at best.
A new cable run is the only option I can see.

Odd, I get 10mm for the hot tub.

What voltage are you basing your calculation on? The load is stated as 6.5kW 26A which only makes sense if that rating is at 250V.
Based on 250V I get 10mm

But if you adjust the load for a 230V supply (assuming the majority of that load is heating and so resistive) it will be running at 5.5kW and 24A and again I get 10mm as being suitable.
 
Feel bit sorry for bloke and doubt he will pay for upgrade, and im not planning on doing works.
Was just thinking if in theory by doubling the existing cores would improve the current installation.

Yes doubling up the 4 core will improve the situation, it may not make it perfect but it will improve it.

But does the hot-tub work currently? If it does then it suggests that the volt drop is not currently so excessive that it will cause a functional issue.
Does the hot tub have a minimum supply voltage rating? (rememeber the percentages given in the regs are intended for use when the voltage tolerance of a load is unknown, not necessarily a hard limit for every circuit)

Obviously the fact that something works in its current states doesn't guarantee safety, but it does indicate that the supply may be functionally adequate.

Have you measured the voltage drop on the hot tub circuit?
 
Odd, I get 10mm for the hot tub.

What voltage are you basing your calculation on? The load is stated as 6.5kW 26A which only makes sense if that rating is at 250V.
Based on 250V I get 10mm

But if you adjust the load for a 230V supply (assuming the majority of that load is heating and so resistive) it will be running at 5.5kW and 24A and again I get 10mm as being suitable.
Let me do it again. I think I may have used 32 amps as the load...

Edit:
Recalculated using 26 amps, still get 16mm² due to volt drop.

Edit 2:
I used installation method D1 assuming an underground cable run.
 
Last edited by a moderator:

Reply to Swa install to hot tub in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top