FCC5206

Evening all
I have been asked what size cable will be required for a long run. I know there are heaps of threads on here from people too lazy to do their homework but I have and am still lost so sorry if this has been covered i just cant find the answer.
The run is to power a stable block which the customer has told me needs power equivalent to a 2 bed house!!
The length of the run is 140 meters!
Taking into consideration max demand and diversity after doing my voltdrop calcs i come up with a 2 core 95mm2 to achieve the required 5% drop!! I know this is absurd and was wondering if anyone could point me in the right direction

Thanks

Chris
 
This is what we came up with shower, cooker, kitchen ring, ring for the rest of the building, lighting and he specifically said underfloor heating! He is not the easiest to deal with as he says “take the worst case scenario” but who know what that means.
I think his idea is to use it for stable hands etc but will never say due to planning constraints.
 
The existing house if fed by 100A. I havent thought what i would allow for as i didnt like the calculations i was getting, i know this is a cop out but i didnt know if this kind of construction is to big for the existing set up.
 
After looking into it in more detail as money appears to be no problem to the owner this would have to be a consideration. I want to make sure I am not making any mistakes before giving a job away!!
 

Reply to SWA long 140M run please help!! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
921
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...
Replies
4
Views
2K
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top