A new build bungalow is 180m from the meter position (single phase meter in hut at the side of the road). There are 2x SWA from meter to a join next to the bungalow, where the supply then enters an external meter cupboard in 25mm SWA (new colours).
The two cables from the meter to the join are 1x 6mm 2C and 1x 16mm 2C (Red & black).
When I first entered site the building was already constructed, and that supply arrangement already present.
I have been to second fix, the builder was *sure* that the supply install had been done by a proper local firm (wont name here). After inspection it is evident that this isnt the case as there were no glands on any cable ends, no fused isolator or RCD or earth rod anywhere.
There is a static caravan and stables also on the site, which appear to be fed via the 6mm and 16mm SWAs from a join *somewhere* underground.
I have already been paid for 1st and 2nd fix, and stated that I wouldn't sign the job off unless the supply was adequate.
I have installed a 60A switch fused isolator and 100mA S type RCD & rod at the origin as a quick improvement to the situation and managed to gland the cables, however the cable run is obviously too far for 6 & 16 mm cables.
What would be the best way to proceed? To work out a suitable cabling arrangement from meter or to get the electric board to move the meter position to the bungalow?
The two cables from the meter to the join are 1x 6mm 2C and 1x 16mm 2C (Red & black).
When I first entered site the building was already constructed, and that supply arrangement already present.
I have been to second fix, the builder was *sure* that the supply install had been done by a proper local firm (wont name here). After inspection it is evident that this isnt the case as there were no glands on any cable ends, no fused isolator or RCD or earth rod anywhere.
There is a static caravan and stables also on the site, which appear to be fed via the 6mm and 16mm SWAs from a join *somewhere* underground.
I have already been paid for 1st and 2nd fix, and stated that I wouldn't sign the job off unless the supply was adequate.
I have installed a 60A switch fused isolator and 100mA S type RCD & rod at the origin as a quick improvement to the situation and managed to gland the cables, however the cable run is obviously too far for 6 & 16 mm cables.
What would be the best way to proceed? To work out a suitable cabling arrangement from meter or to get the electric board to move the meter position to the bungalow?