E.E.I
-
I wouldn't terminate the cpc through the isolator switch, make sure the isolator has a separate earth terminal/earth bar. Having a separate MET would look messy IMO.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Swa main incomer size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Yes the people ordering the work said 25mm 3 core. How ever I think that's a general spec rather than specific which we are struggling to get hold off.
Also if it's a 3 core and terminate the cpc in the isolator once this is isolated there would be no earth at the cu. would you install spectate met at isolator end too?
isolators have an earth+neutrel terminal mate that isnt isolated by isolatorYes the people ordering the work said 25mm 3 core. How ever I think that's a general spec rather than specific which we are struggling to get hold off.
Also if it's a 3 core and terminate the cpc in the isolator once this is isolated there would be no earth at the cu. would you install spectate met at isolator end too?
our 4pole isolators early make, late breakNot always, a Double pole or a TPSN/four pole isolator isolates the neutral.
And most plug and socket arrangements used for isolation will isolate the earth.
our 4pole isolators early make, late break
have a seperate earth and n connection as well mate.
buy a different brand then mate
really? we have controls going through our isolators as well sometimes depending on specWhy would you need a seperate N in a four pole isolator? That's what the fourth pole is there for!
And I am quite happy with the brand if isolator I use, MEM are tried and tested.
It would be great if people learnt the difference between 3P+N and 4P. As Shanky rightly said in a 3P+N the neutral is early make late break. The reason, because you will get voltage imbalance akin to a floating neutral.
I’ve only ever specified four pole ACB/MCCB’s twice in 40 years.
Both breakers were for a 2.6MW 660V two wire earth free system. Four pole because I put two poles in series to handle the fault current. If you look at the manufacturer’s maximum fault current tables for 400V against 690V it drops dramatically!
For Christ’s sake!
You use 3P+N or SP+N never 4P for distribution!