I wouldn't terminate the cpc through the isolator switch, make sure the isolator has a separate earth terminal/earth bar. Having a separate MET would look messy IMO.
 
Yes the people ordering the work said 25mm 3 core. How ever I think that's a general spec rather than specific which we are struggling to get hold off.
Also if it's a 3 core and terminate the cpc in the isolator once this is isolated there would be no earth at the cu. would you install spectate met at isolator end too?


Are you actually being serious here??

You follow the Spec that was issued as part of the contract details the job was priced against, any retrospect amendments to that spec (eg, any so-called specific spec) then both contractual parties would need to agree on any changes made, along with any increase/decrease in the contract price...
 
Personally I’d let him go ahead and change the spec. I used to get a perverse pleasure out of telling a contractor to rip it out and do it again at their expense.
 
Yes the people ordering the work said 25mm 3 core. How ever I think that's a general spec rather than specific which we are struggling to get hold off.
Also if it's a 3 core and terminate the cpc in the isolator once this is isolated there would be no earth at the cu. would you install spectate met at isolator end too?
isolators have an earth+neutrel terminal mate that isnt isolated by isolator
 
Not always, a Double pole or a TPSN/four pole isolator isolates the neutral.
And most plug and socket arrangements used for isolation will isolate the earth.
 
our 4pole isolators early make, late break

have a seperate earth and n connection as well mate.

buy a different brand then mate

Why would you need a seperate N in a four pole isolator? That's what the fourth pole is there for!

And I am quite happy with the brand if isolator I use, MEM are tried and tested.
 
Having controls through a pole of an isolator sounds quite unusual.
Id expect to see control circuits use auxiliary contacts, but then I guess it depends on the equipment and budget.
 
It would be great if people learnt the difference between 3P+N and 4P. As Shanky rightly said in a 3P+N the neutral is early make late break. The reason, because you will get voltage imbalance akin to a floating neutral.




I’ve only ever specified four pole ACB/MCCB’s twice in 40 years.

Both breakers were for a 2.6MW 660V two wire earth free system. Four pole because I put two poles in series to handle the fault current. If you look at the manufacturer’s maximum fault current tables for 400V against 690V it drops dramatically!
 
It would be great if people learnt the difference between 3P+N and 4P. As Shanky rightly said in a 3P+N the neutral is early make late break. The reason, because you will get voltage imbalance akin to a floating neutral.
I’ve only ever specified four pole ACB/MCCB’s twice in 40 years.

Both breakers were for a 2.6MW 660V two wire earth free system. Four pole because I put two poles in series to handle the fault current. If you look at the manufacturer’s maximum fault current tables for 400V against 690V it drops dramatically!


Yep, all our 2.5-3.2 KA main switchboard TX ACB incomers and the bus couplings are 3 Pole + N with the early make late break function.
 

Reply to Swa main incomer size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
745
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
974

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
608
No table I just know the conductivity of the armour is around 4.0mm² copper equivalent so 6.0mm² will be fine.
Replies
6
Views
450

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top