Hi,

Im hearing contridicting info on this.

When i was in college my tutor told me if SWA was used in a way as it was 3 core and one the cable was the earth then the SWA only needs earth glanding and fly cable on one side of the terminated SWA. But ive seen a couple PIRs pick this up as a fault as needing amended to earthed with fly cable both sides.

which is correct?

Obv it cant never hurt to do both sides, but does one side in this case meet regulations?
 
SWA needs a proper gland at every termination.
If the armour is not used as the cpc then it only requires bonding at one end.
 
What exactly was the observation on the report?
Was it the lack of a proper gland or the lack of an earth connection? You didn't make that clear in the OP
 
yeah exactly what i thought.

Maybe it only been picked up on PIRs i seen then as they just over looked it.

lack of earth gland and fly cable but on attendance it was only one side that lacked it
 
I worked in a factory and the armoring's in every cable was used for earth (which I totally disagree with the glanding is appalling) and flyings on both ends which I would do no matter what, If it was cpc or not.
 
I worked in a factory and the armoring's in every cable was used for earth (which I totally disagree with the glanding is appalling) and flyings on both ends which I would do no matter what, If it was cpc or not.

Why?? Depending on the size and number of cores, the armouring meets all the requirements as that circuits CPC. The only time the armouring won't comply (in most cases) is if it is also going to be used for main bonding purposes.... So there's nothing to really disagree with here!!
 
Why?? Depending on the size and number of cores, the armouring meets all the requirements as that circuits CPC. The only time the armouring won't comply (in most cases) is if it is also going to be used for main bonding purposes.... So there's nothing to really disagree with here!!
The glanding is so bad armourings are above the gland on CWs, if your going to do it your glanding as to be the best, I've even saw shrouds cut and taped at the back.
 
The glanding is so bad armourings are above the gland on CWs, if your going to do it your glanding as to be the best, I've even saw shrouds cut and taped at the back.

As rough as it looks and is the fact that the shroud is damaged is not going to affect the armour functioning as a cpc.

As for the armour being exposed outside of a CW gland, well that is just wrong and the termination is compromised whatever is being used as the cpc.
 
As rough as it looks and is the fact that the shroud is damaged is not going to affect the armour functioning as a cpc.

As for the armour being exposed outside of a CW gland, well that is just wrong and the termination is compromised whatever is being used as the cpc.

My point is if your willing to gland that badly what else have you bypassed done badly
 
Originally Posted by jp1976 I worked in a factory and the armoring's in every cable was used for earth (which I totally disagree with .

I was querying your statement above, not the state of the terminations that you found...
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
North

Thread Information

Title
SWA need fly cable both ends
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
13

Thread Tags

Tags Tags
cable swa

Advert

Thread statistics

Created
paulthemagpie,
Last reply from
Engineer54,
Replies
13
Views
4,058

Advert

Back
Top