Hi All got a call today some one wants a socket, out side using. 32 amp and swa trying to work out the size of the swa got a amind blank any help would be gratefull:eek:
 
C'est simple how many meter in distance that will really affect the voltage drop I useally keep it under 5% voltage drop

Useally first 30 meter is not super circital unless it loaded near 32 amp all the time but any longer than 30 meter or longer you will have to increase the conductor size to compense the voltage drop

under 30 meter distance you can use 6.0mm² unless your local code say something else but if that circuit will be plan to increase the load in the future you will have to take a acount of upsizing and the SWA cable size as well I know normally I can get SWA in France the smallest one I useally use is 10mm² or larger.

Merci,Marc
 
Hi...Yes, 4mm (copper conductor) should be ok, single-phase or 3-phase for 32A. However, make sure that you have one of the cores available as a CPC, and do not use the armour as the CPC as this will increase the csa requirements of the cores.

Yooj
 

Reply to swa outside in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
707
  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
636
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top