Could anyone give r1r2 values per metre for 3core 35mm SWA also incorporating the armour as a protective conductor?

The figures I've obtained are 0.00282 but I'm unsure if this incorpartes the armour.

It's to supply a bungalow but the meter and cut out is 160 metres from the house itself.
Thankyou
 
im going from memory here but I get 0.53 Ohms at 160 meters without factoring conductor operating temp at 70 degrees which would be roughly 0.64 this is a proper smoke packet calculation though.
 
I'm going to measure ze tomorrow would anyone be willing to help me with my calculations?
Originally Sp energy where going to supply to the house, somewhere along the way but after I had started the rewire of the property the owner decided to supply his own cable and feed it off the meter 160 metres away.
 
Boozey lunch to be noted, so no warranty :) - a single 35mm conductor is 0.524 mOhm/m at 20C (OSG table I1). So for 160m at 20C without armour you should see about 0.169 Ohm when looped. Putting armour in parallel with one leg is = 0.524+(0.524//Armour) mOhm/m. Armour is 70mm of steel (GN1 table D10b) which for disconnection purposes is equivalent to 31mm Cu (same table) or about 8mm Cu for resistance. Doing resistance calc the 8mm Cu is about 2.46 mOhm/m. So I calc the resistance of 160m of looped 35mm and armour (in parallel with one leg) at 20C to be ... 0.153 Ohm ... ha ... maybe. Anyone been drinking too?
 
Hi , if you use the resistance values from cable manufacturers like Batt cables then the resistance of 35mm is 0.524 and the resistance for the armouring is 2.1 .
So 160 x 0.524 x 1.2 (70 degrees ) /1000 =0.10
160 x 2.1 x 1.18 (60 degrees ) / 1000 = 0.39
therefore 0.10 + 0.39 = 0.49
 

Reply to SWA r1r2 35mm ... ..... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
993

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top