Hi guys,

how would you code a SWA cable which feeds a DB within a commercial unit with no seperate CPC so only realying on the SWA strands as means of CPC
 
Hi guys,

how would you code a SWA cable which feeds a DB within a commercial unit with no seperate CPC so only realying on the SWA strands as means of CPC

Are you saying you have performed calculations which proves that the SWA is not sufficient for use as a CPC ?
 
Last edited:
Hi guys,

how would you code a SWA cable which feeds a DB within a commercial unit with no seperate CPC so only realying on the SWA strands as means of CPC

If it is only a CPC then it is almost certainly compliant (unless your testing suggests otherwise) with current regulations.

If it is also required to perform the function of a main bond then you will need to do further calculations and consider other variables to confirm that it is ok.
 
Hi guys,

how would you code a SWA cable which feeds a DB within a commercial unit with no seperate CPC so only realying on the SWA strands as means of CPC


What size is the SWA is it 2 core 3 core or what, seem to recall that up to and including 95mm 2 core is the limit for using the steel as the cpc, I have a table somewhere giving details, but to busy at the mo to look for it, I got it from Google a while back try (pvc xlpe)
 
Last edited:
What size is the SWA is it 2 core 3 core or what, seem to recall that up to and including 95mm 2 core is the limit for using the steel as the cpc, I have a table somewhere giving details, but to busy at the mo to look for it, I got it from Google a while back try (pvc xlpe)

Be wary of the tables floating around the Internet, they aren't exactly correct, more of a rough guide.
Calculation is the only real way of proving it
 
I personally dont like relying on the SWA although regs are quite happy about it. Always scared SWA comes loose on gland.
Are other forum members comfortable with only the SWA ?

I would be as comfortable and confident in using SWA as a CPC as I am in dressing in and making off SWA glands.
 
I personally dont like relying on the SWA although regs are quite happy about it. Always scared SWA comes loose on gland.
Are other forum members comfortable with only the SWA ?
Wouldn't your concerns be applicable to any earthing application, they are only as good as the method and means in which they are terminated and the competence of the person doing the termination, SWA glands are perfectly fine for the job, its down to the installer to ensure the glands (s)he fits do actually fit the cable correctly and are tight, and where required, an earth tail fitted to the earthing lug or bar.
 
This question smacks of someone carrying out periodic inspection and testing without the knowledge and experience to be doing so. It's amazing how often people comdemn situations which are fully compliant with BS 7671.
 

Reply to SWA seperate CPC in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
273
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
267
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
674
  • Question
It's the same with any system, if you put poo in, you get poo out!
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top