SWA sheath used as main Earth | on ElectriciansForums

Discuss SWA sheath used as main Earth in the Electrician Talk | All Countries area at ElectriciansForums.net

B

Bonse

Hi guys

I recently installed a submain and fed it with 16mm 2 core SWA XLPE and used the sheath as an earth....

does anyone know the calculation to work out the equivalent conductor size ? i know it works out to be approx 35mm.

Hope that question makes sense.

Darren
 
Bonse iv got a PDF of SWA CPC values in box me your email addy and i ll send it to you :D
The equation is on there as well.
 
Last edited by a moderator:
This link is a paper written by John Peckham, a well respected Chartered Engineer. It will give you a very good basic understanding on the subject.
The tables for both thermoplastic and thermosetting SWA cables will give more realistic results, without the need for any further calculations, that may be required by the other table posted here earlier....

I have personally been using these 2 tables for almost 4 years now, they are good to go... lol!!!

http://www.electriciansforums.net/a...an-we-use-armour-swa-cpc-using-armour-swa.pdf
 
I don’t know if it’s still possible but at one time you could specify high conductivity armour. One armour in say 4 or 5 would be copper. We used these a lot under M&Q regs. The copper would be just a tad bigger that the steel as it would flatten down in the gland. You would only get them if you went over 120mm cable.
I’ll say I’ve never run a separate CPC with a cable but with one proviso, on many large cable trays within a switch room I would run a 1x1/8” copper tape bolted all along the tray, this could be joined on to for any cable or enclosure.

One switch room I modified had two incoming feeds, one @550V via a 0.3” 3c PILCSWA, the other @440V via a 195mm 3+1/2c SWA (high conductivity) both boards shared the same main cable tray, so both linked via the earth tape. I never worried about earth paths in there.
 
Thanks everyone for the replies. ive only just managed to get back to my computer! will have to sort that damn phone out lol
 

Reply to SWA sheath used as main Earth in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

You would treat it as a TT installation.
2
Replies
29
Views
1K
I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
564
Sounds more positive.
Replies
8
Views
472
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
  • Question
in the day of 2c cable we used the same size earth fly lead as the line cores never bothered to work it out
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks