So I’m an inexperienced novice and I accept I know two ninths of four fifths of FA but when was this arrangement ever ok?
Installing like for like replacement garden lights, currently connected to a run of 4 core 1.5mm SWA emerging from ducting under patio. Somewhere further back it’s joined to lighting circuit and then back to 6A RCBO.
Brown and blue cores utilised for L and N of lights.
Grey and Black cores are also put to use, as L and N for an outdoor 13A socket at the end of the garden. The armour is providing the cpc and zs measurements at lights show it’s doing a fine job.
The switch for the garden lights also disconnects the line to the outside socket.
Am I missing something here? I’ve told clients that the socket has to go.