Hi
Fitting a consumer unit in garage . Unfortunately the 16MM SWA is too short to reach consumer unit
So i have done as follows .

Glanded SWA into a metal adaptable box .
earthing nut earthed with 10mm crimped and run to earth block .
2 cores of SWA Brown and Grey ( oversleeved BLUE) run to single pole Henley blocks
25mm LIVE and Neutral tails to consumer Unit main switch through Same 32 mm hole
3rd core of SWA ( oversleeved earth ) to earthing Block in consumer unit .

Everything is being boxed over ( acessable ) so the single insulated cores of SWA will be covered.

Does this seem ok?

Also at the supply end is it okay 25mm tails from henley to 100amp double isolator to feed swa after glanding in a adaptable box .
Thanks
 
Confirm it with the Electrician, I didn't realise you were in tally with an electrician, don't worry about the supply characteristics then as this should have also been taken into account by your electrician, in hindsight it would have been better to get them in to do the extended joint as in its present state it would not comply as others have mentioned.
 
The CPC and neutral are connected to the same block of brass in the DNO service head on a TNCS system, so any Ze you measure at the CU will be just the resistance of the two tails, which for a 'normal' set up will be very close to zero.
On a TNS system, the connection point between the two is further back the line, so you should be able to measure a significant resistance.
 

Reply to SWA too short ! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
312
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
941

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
710
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top