E
Engineer54
The table is correct 100% correct... as for confusing im not sure what you mean as long as you de-rate your XLPE to 70c as it clearly states 90c .... please dont tell me we have to further simplify these things wheres the technical part gone from been an Electrician if they never do the calculations and get drip fed all the answers how can their be any competence anymore....
Ill agree though i should have pointed that out about the Temp' de-rating on the XLPE may show compliance using the adiabatic equation where due to the 90c rating it shows as a non-compliance.
That earthnuts table has been around forever and a day, and to my knowledge has never been updated since the 80's!! So are you sure, it's 100% correct?? What's the point of having a table if you are going to have to recalculate every value it gives you?? Surely tables are for convenience, i can quite happily calculate for all the values i need, as should all competent electricians. Doesn't mean that a convienient table isn't going to be usefull to electricians and the like.
I've been using this table for a few years now, it has been updated and has taken most of the need for re-calulation away. That's if we are looking at SWA being used solely as the CPC, and not as the main earthing conductor, that will be also be catering for main bonding conductors of extraneous services and metalwork....
Blue = min CSA of cables SWA to comply.
(Red) = Cable does not comply.
Table for 70[SUP]0[/SUP]C Thermoplastic PVC SWA cables.
[TABLE="class: yiv9896119791cms_table_yiv1559363916MsoTableGrid"]
[TR]
[TD="width: 118"]
Conductor CSA
[TD="width: 118"]
Minimum CSA of SWA to meet 54G
[TD="width: 118"]
CSA of armour 2 core
[TD="width: 118"]
CSA of armour 3 core
[TD="width: 118"]
CSA of armour 4 core
[/TR]
[TR]
[TD="width: 118"]
1.5
[TD="width: 118"]
3.4
[TD="width: 118"]
15
[TD="width: 118"]
16
[TD="width: 118"]
17
[/TR]
[TR]
[TD="width: 118"]
2.5
[/TD][TD="width: 118"]
5.7
[TD="width: 118"]
17
[TD="width: 118"]
19
[TD="width: 118"]
20
[/TR]
[TR]
[TD="width: 118"]
9.0
[TD="width: 118"]
21
[TD="width: 118"]
23
[TD="width: 118"]
35
[/TR]
[TR]
[TD="width: 118"]
13.6
[TD="width: 118"]
24
[TD="width: 118"]
36
[TD="width: 118"]
40
[/TR]
[TR]
[TD="width: 118"]
22.6
[TD="width: 118"]
41
[TD="width: 118"]
44
[TD="width: 118"]
49
[/TR]
[TR]
[TD="width: 118"]
16
36.1
[TD="width: 118"]
46
[TD="width: 118"]
50
[TD="width: 118"]
72
[/TR]
[TR]
[TD="width: 118"]
25
36.1
[TD="width: 118"]
60
[TD="width: 118"]
66
[TD="width: 118"]
76
[/TR]
[TR]
[TD="width: 118"]
35
36.1
[TD="width: 118"]
66
[TD="width: 118"]
74
[TD="width: 118"]
84
[/TR]
[TR]
[TD="width: 118"]
50
56.4
[TD="width: 118"]
74
[TD="width: 118"]
84
[TD="width: 118"]
122
[/TR]
[TR]
[TD="width: 118"]
70
79.0
[TD="width: 118"]
84
[TD="width: 118"]
119
[TD="width: 118"]
138
[/TR]
[TR]
[TD="width: 118"]
95
107.2
[TD="width: 118"]
122
[TD="width: 118"]
138
[TD="width: 118"]
160
[/TR]
[TR]
[TD="width: 118"]
120
135.3
[TD="width: 118"]
(131)
[TD="width: 118"]
150
[TD="width: 118"]
220
[/TR]
[TR]
[TD="width: 118"]
150
169.2
[TD="width: 118"]
(144)
[TD="width: 118"]
211
[TD="width: 118"]
240
[/TR]
[TR]
[TD="width: 118"]
185
208.6
[TD="width: 118"]
(201)
[TD="width: 118"]
230
[TD="width: 118"]
265
[/TR]
[TR]
[TD="width: 118"]
240
270.6
[TD="width: 118"]
(225)
[TD="width: 118"]
(260)
[TD="width: 118"]
299
[/TR]
[TR]
[TD="width: 118"]
300
338.3
[TD="width: 118"]
(250)
[TD="width: 118"]
(289)
[TD="width: 118"]
(333)
[/TR]
[TR]
[TD="width: 118"]
400
403.9
[TD="width: 118"]
(279)
[TD="width: 118"]
(319)
[TD="width: 118"]
467
[/TR]
[/TABLE]
Table for 90[SUP]0[/SUP]C Thermosetting SWA cables operating at 70[SUP]0[/SUP]C.
[TR]
[TD="width: 118"]
Conductor CSA
[TD="width: 118"]
[TD="width: 118"]
[TD="width: 118"]
[/TR]
[TR]
[TD="width: 118"]
1.5
[TD="width: 118"]
3.4
[TD="width: 118"]
16
[TD="width: 118"]
17
[TD="width: 118"]
18
[/TR]
[TR]
[TD="width: 118"]
2.5
5.7
[TD="width: 118"]
17
[TD="width: 118"]
19
[TD="width: 118"]
20
[/TR]
[TR]
[TD="width: 118"]
9.0
[TD="width: 118"]
19
[TD="width: 118"]
21
[TD="width: 118"]
23
[/TR]
[TR]
[TD="width: 118"]
13.6
[TD="width: 118"]
22
[TD="width: 118"]
23
[TD="width: 118"]
36
[/TR]
[TR]
[TD="width: 118"]
22.6
[TD="width: 118"]
26
[TD="width: 118"]
39
[TD="width: 118"]
43
[/TR]
[TR]
[TD="width: 118"]
16
36.1
[TD="width: 118"]
41
[TD="width: 118"]
44
[TD="width: 118"]
49
[/TR]
[TR]
[TD="width: 118"]
25
36.1
[TD="width: 118"]
42
[TD="width: 118"]
62
[TD="width: 118"]
70
[/TR]
[TR]
[TD="width: 118"]
35
36.1
[TD="width: 118"]
62
[TD="width: 118"]
70
[TD="width: 118"]
80
[/TR]
[TR]
[TD="width: 118"]
50
56.4
[TD="width: 118"]
68
[TD="width: 118"]
78
[TD="width: 118"]
90
[/TR]
[TR]
[TD="width: 118"]
70
79.0
[TD="width: 118"]
80
[TD="width: 118"]
90
[TD="width: 118"]
131
[/TR]
[TR]
[TD="width: 118"]
95
107.2
[TD="width: 118"]
113
[TD="width: 118"]
128
[TD="width: 118"]
147
[/TR]
[TR]
[TD="width: 118"]
120
135.3
[TD="width: 118"]
(125)
[TD="width: 118"]
141
[TD="width: 118"]
206
[/TR]
[TR]
[TD="width: 118"]
150
169.2
[TD="width: 118"]
(138)
[TD="width: 118"]
201
[TD="width: 118"]
230
[/TR]
[TR]
[TD="width: 118"]
185
208.6
[TD="width: 118"]
(191)
[TD="width: 118"]
220
[TD="width: 118"]
255
[/TR]
[TR]
[TD="width: 118"]
240
270.6
[TD="width: 118"]
(215)
[TD="width: 118"]
(250)
[TD="width: 118"]
289
[/TR]
[TR]
[TD="width: 118"]
300
338.3
[TD="width: 118"]
(235)
[TD="width: 118"]
(269)
[TD="width: 118"]
(319)
[/TR]
[TR]
[TD="width: 118"]
400
451.0
[TD="width: 118"]
(265)
[TD="width: 118"]
(304)
[TD="width: 118"]
452
[/TR]
[/TABLE]
Notice, that the 90'c thermosetting cables table, has already been adjusted for 70'c operation...