Hi Guys

Been to look at a job, as follows :

  • Existing Swimming Pool House 20meters away from main house, DB in here on TT set up, Ze = 90ohms.
  • Plan is to come off here to supply another outbuilding which is about 15metres away.

Just wanting to make sure DB I'm coming off of is compliant, as I'll potentially be the last one touching it.

Looking through section 702, seen 702.410.3.4.3(ii) mentions a figure of 20ohms or less if using an electrode to backup PME - that confuses me as thought you couldn't mix the two ! Which leads on to the question of with the Ze of 90ohms, is this ok as its under 200ohms or does it have to be under 20ohms ?

Hopefully this makes sense - sorry its been one of them days.

Cheers Sy ;-)
 
Looking through section 702, seen 702.410.3.4.3(ii) mentions a figure of 20ohms or less if using an electrode to backup PME - that confuses me as thought you couldn't mix the two ! Which leads on to the question of with the Ze of 90ohms, is this ok as its under 200ohms or does it have to be under 20ohms ?

What do you mean by can't mix the two? Yes they recommend a sub 20ohm Ra if connecting an earth electrode to a PME system, that's not mixing anything though, just connecting an earth electrode.

Is 90ohms a normal value for a TT system in this area? Does it seem unusual or is it what you would expect to get from a good earth electrode setup in your area?

Are you able to determine how many rods have been used to make up the earth electrode for this TT supply?
 
What do you mean by can't mix the two? Yes they recommend a sub 20ohm Ra if connecting an earth electrode to a PME system, that's not mixing anything though, just connecting an earth electrode.

Is 90ohms a normal value for a TT system in this area? Does it seem unusual or is it what you would expect to get from a good earth electrode setup in your area?

Are you able to determine how many rods have been used to make up the earth electrode for this TT supply?

Cheers Dave.... 90 is normal around here.
Regards to PME and earth electrtode together, always good to check thank you for clarifying ;-)
 

Reply to Swimming Pool Regs 702 in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top