Hi Guys
Been to look at a job, as follows :
Just wanting to make sure DB I'm coming off of is compliant, as I'll potentially be the last one touching it.
Looking through section 702, seen 702.410.3.4.3(ii) mentions a figure of 20ohms or less if using an electrode to backup PME - that confuses me as thought you couldn't mix the two ! Which leads on to the question of with the Ze of 90ohms, is this ok as its under 200ohms or does it have to be under 20ohms ?
Hopefully this makes sense - sorry its been one of them days.
Cheers Sy ;-)
Been to look at a job, as follows :
- Existing Swimming Pool House 20meters away from main house, DB in here on TT set up, Ze = 90ohms.
- Plan is to come off here to supply another outbuilding which is about 15metres away.
Just wanting to make sure DB I'm coming off of is compliant, as I'll potentially be the last one touching it.
Looking through section 702, seen 702.410.3.4.3(ii) mentions a figure of 20ohms or less if using an electrode to backup PME - that confuses me as thought you couldn't mix the two ! Which leads on to the question of with the Ze of 90ohms, is this ok as its under 200ohms or does it have to be under 20ohms ?
Hopefully this makes sense - sorry its been one of them days.
Cheers Sy ;-)