Hello, Ive been doing some work for a neighbour who has just moved into a house with a swimming pool, i couldnt help but have a look at the wiring for the pool ect, the pool is heated by a gas boiler and has a electric pump, this was fitted last year and has been signed off.
The problem i have with it is the supply is tncs and i know that all swimming pool equipment wasnt allowed to be installed on to this type of supply, so i thought id rang the sparky that installed it to see what he said, the reply i got was 'because its only the pump then its ok'.

Is he right with this ?

thanks jimmy
 
7671 does not prevent a TNCS supply being used for a pool,however depending on the zone it may be neccessary to install a bonded grid which is not generally practical...702.410.3.4.3.
As long as the pump is outside the zones and the pipework into the pool is plastic a TNCS supply can be used.....section 702 needs to be consulted to get the full picture though.
 
Im going to mention it for old times sake, as above regards 7671 but the only concern is a broken PEN Conductor. However a small voltage difference between the PME earthing terminal at the origin of an installation and true Earth potential may exist.
This Small voltage above Earth potential could under certain conditions such as reduced body resistance due to the presence of water, create the posibility of a perceived electric shock for a person in contact with a conductive part(a handrail connected to the supplementary bonding) and earth Potential ( ie,uninsulated Wet floor etc.) Swimming Pool may be made a TT system,where the exposed conductive parts and extraneous conductive parts are seperated from the PME earthing Terminal.
 
You wouldn't normally connect the pool earthing arrangement ( concrete re-bar, earth rods etc) to a PME derived system, they would remain separated. Nothing stopping you using a PME system to supply the pool pumps, heaters banks etc, they will normally be located outside of the zones anyway.

If the pool system was supplied from a TN-S or TT system, then the pool earthing arrangements can be bonded back to the pool installations EMT. ...My earthing system is TT so my pool is bonded back via the EMT to the MET which in turn gives me an extremely good overall Ra value to my installation....
 
You wouldn't normally connect the pool earthing arrangement ( concrete re-bar, earth rods etc) to a PME derived system, they would remain separated. Nothing stopping you using a PME system to supply the pool pumps, heaters banks etc, they will normally be located outside of the zones anyway.

If the pool system was supplied from a TN-S or TT system, then the pool earthing arrangements can be bonded back to the pool installations EMT. ...My earthing system is TT so my pool is bonded back via the EMT to the MET which in turn gives me an extremely good overall Ra value to my installation....

Old thread I know, But as someones brought it back to life i will coment. As E54 Says great stuff. But I wonder why people are happy to connect hot tubs up without such thought..
 

Reply to Swimming pool in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
888
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Some year back there was a case of a young girl killed by being sucked down to the bottom of a pool when being emptied through the power drain...
2
Replies
23
Views
1K
I am confronted by people with experience in using them for lighting circuits and sockets in a three-phase installation, as it is only allowed to...
Replies
0
Views
172

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top