New position of replacement Consumer Unit for my customer is now going to be 7m away from the supply head. DNO fuse is 100A BS1361 and this is a large house so I still need a (potential) 100A supply. I believe that I am supposed to fit a switch fuse if tails are over 3m long. Firstly, am unclear if this is a regulation or just an undocumented 'DNO requirement'. Secondly, can anyone recommend a make and model of switchfuse suitable for use in a domestic environment? Am concerned about aesthetics (it might have to be on show) and cost - I see some commercial/industrial ones cost £100s. Presumably the enclosure would have to be of metal construction, though that is not clear either. Which ones have you fitted and what is your opinion of them? One other point - if I fit a 100A switchfuse, how will that discriminate (select?) before the DNO supply head fuse?
 
New position of replacement Consumer Unit for my customer is now going to be 7m away from the supply head. DNO fuse is 100A BS1361 and this is a large house so I still need a (potential) 100A supply. I believe that I am supposed to fit a switch fuse if tails are over 3m long. Firstly, am unclear if this is a regulation or just an undocumented 'DNO requirement'. Secondly, can anyone recommend a make and model of switchfuse suitable for use in a domestic environment? Am concerned about aesthetics (it might have to be on show) and cost - I see some commercial/industrial ones cost £100s. Presumably the enclosure would have to be of metal construction, though that is not clear either. Which ones have you fitted and what is your opinion of them? One other point - if I fit a 100A switchfuse, how will that discriminate (select?) before the DNO supply head fuse?
I agree a switch fuse is a good idea, I like Schnieder but you will have plenty of choice, speak to your wholesaler mate.
 
Hi - could try this Wylex one
Wylex 100 Amp SP&N Switchfuses - https://www.tlc-direct.co.uk/Manufacturers/Wylex/Switchfuse_SP_and_N/index.html

[ElectriciansForums.net] Switch fuse for tails
 
To MDJ - Oh dear - is this now going to turn into a slanging match? I hope not. A genuine contractor here asking a genuine question about a real-life on-the-job scenario. As a sole-trader it is at times difficult to know exactly what to do for the best in some circumstances, hence my question. If you do not have a sensible answer then please refrain from muddying the waters further with your unhelpful response.
 
To MDJ - Oh dear - is this now going to turn into a slanging match? I hope not. A genuine contractor here asking a genuine question about a real-life on-the-job scenario. As a sole-trader it is at times difficult to know exactly what to do for the best in some circumstances, hence my question. If you do not have a sensible answer then please refrain from muddying the waters further with your unhelpful response.
Not at all it was a bit of fun, and I gave you a answer afterwards, I thought your question was a good one, you have now had 2 answers, regarding the 2nd one, the wylex unit is also decent, there are dozens of types, I prefer the type where there is room around the busbar, in general these switch fuses are tight and seem to get smaller, not sure about BG which is the cheaper option, at 7 mtrs of tails a switch fuse is a requirement.
 
Thank you for a now helpful response. Someone else suggested Schneider but no model name given. Yes, I can ask my wholesaler but they are only likely to suggest whatever they have in stock. I am looking for recommendations of what others have successfully used. A model number would be useful so I can google it and see what they look like.
 
Thank you for a now helpful response. Someone else suggested Schneider but no model name given. Yes, I can ask my wholesaler but they are only likely to suggest whatever they have in stock. I am looking for recommendations of what others have successfully used. A model number would be useful so I can google it and see what they look like.
How much room have you got in the area where the switch fuse will be fitted?
 
New position of replacement Consumer Unit for my customer is now going to be 7m away from the supply head. DNO fuse is 100A BS1361 and this is a large house so I still need a (potential) 100A supply. I believe that I am supposed to fit a switch fuse if tails are over 3m long. Firstly, am unclear if this is a regulation or just an undocumented 'DNO requirement'. Secondly, can anyone recommend a make and model of switchfuse suitable for use in a domestic environment? Am concerned about aesthetics (it might have to be on show) and cost - I see some commercial/industrial ones cost £100s. Presumably the enclosure would have to be of metal construction, though that is not clear either. Which ones have you fitted and what is your opinion of them? One other point - if I fit a 100A switchfuse, how will that discriminate (select?) before the DNO supply head fuse?

I've just used a couple of Hamilton HLMFS. Significantly cheaper than the Wylex, seem to be good build quality, 100A maximum, comes with 63A, 80A and 100A fuses. Earth bar easily accommodates 16mm.

Nice units.

I wouldn't worry about discrimination. The switch fuse is there because the DNO won't guarantee their fuse will blow in time in the event of a fault on the tails if they are longer than 3m.
 
well the more room the better, I have a single phase 100 amp MEM switch fuse if you want it, not sure what the P&P would cost but it is immaculate and never used, probably 7-8 years old and industrial but it is yours if the postage is not a problem. In fact I may be wrong it may be an isolator I will have a look.
 
Apologies it looks like an Isolator I will go and take a look and PM you if it is a Switch fuse.
 

Reply to Switch fuse for tails in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
487
  • Question
Yes like that - fitted last week 😂
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top