If an fuses for existing spare switched fuse unit within a switch panel is now obsolete (GEC Alsthom) then is it going to be a case of upgrading the whole panel if I want to add a new circuit?

That could turn a £500 job into about a £10k job.

I suspect I could get the parts off eBay but they probably aren't back by manufacturers warranty any more and don't want to install something that isn't legit.
 
I have been informed it is a 750kVA transformer and the fuses in the CT Chamber are sized at 800 amp. I will be contacting the DNO to get confirmation of this however.

750KVA on a dedicated circuit would have a 1200A SF, 1000A @433V.

I think a call to the DNO is in order. Don’t take this the wrong way, this could turn in to an expensive exercise. Get all the information you can first.

If the CT camber is on the bottom of the MiniForm 800A SF the cover only has 4 screws and is hinged at the bottom and will swing downwards. If you do have a look, be careful.

Cheers, like a said I will be contacting the DNO. The CT Chamber is separate to the MiniForm.
 
I've had a quote from Slaters for a refurbished switch fuse. They provide 18 mths warranty. Going to inform the client and see if they still want the panel upgrading for future works.


There you go!!

If this company can supply refurbished switch fuses, then maybe you won't need to go with replacing the switchboard, you can purchase refurb switch fuse units of the correct rating for the existing empty spare cubicles.
 
They’re still available new. To uprate from 100A to 200A is a five minute job.

Just for information MiniForm is available as 30, 60, 100, 200 and 250A. Only one 250A can be fitted in each vertical row of switches. It must be mounted in the first bay from the busbar chamber.
 
They’re still available new. To uprate from 100A to 200A is a five minute job.

Just for information MiniForm is available as 30, 60, 100, 200 and 250A. Only one 250A can be fitted in each vertical row of switches. It must be mounted in the first bay from the busbar chamber.

Thanks. I'm fitting a 200 amp. Is there any stipulation as to where that can go?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Switch Panel upgrade
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
46
Unsolved
--

Advert

Thread statistics

Created
atm84,
Last reply from
Knobhead,
Replies
46
Views
4,231

Advert

Back
Top