hi guys,
just having a debate over switch wires not being marked up,
one guy says its a code 3
one says if you don't understand what the cable does and where it goes you should not be in the fitting in the first place.
care to comment guys
 
Its a requirement now if the cable is not of a phase colour (earth conductors not to be used for L or N of course), so as you testing to the 17th you will need to code it as suggested, yes also you colleague is correct you should be suitably competent in the first place but the regs are designed to reduce confusion and accidents and this is one area DIYers often balls up as well as the less competent sparks.

When you say ID are we talking about marking up the black (old colours) or the blue (new colours) with a sleeve to identify it as a phase conductor?
 
...Must be a slow news day...if i have to comment,it would be to say how disappointed i would be,if i read a previously completed EICR,with code 3's for missing cable ID's,and everything important Limmed out...
 
If more people would buy the correct cable ie. twin brown PVC/PVC or in old money twin red PVC/PVC then this problem would never be an issue. Always wondered why this is not normal practice on the mainland.
 
A tagged blue gives more information at a glance (i.e. which is L & SL) than twin brown. The browns might be different but not so obvious.
 
hi guys,
just having a debate over switch wires not being marked up,
one guy says its a code 3
one says if you don't understand what the cable does and where it goes you should not be in the fitting in the first place.
care to comment guys
Oh no------------
 

Attachments

  • [ElectriciansForums.net] switch wire I D
    fainted.jpg
    46.6 KB · Views: 101

Reply to switch wire I D in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
461
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
Firstly I would suggest that of the three sets of cables, they are not all 'incoming'. There might be one cable (of 3 wires) bringing in permanent...
Replies
1
Views
776
  • Question
Did it work?
Replies
3
Views
733

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • Borrowed earth
    If mechanily protected would a 2.5 not suffice.you could manufacture metal conduit just to get...
  • Duplicate posts
    Any suggestions for avoiding the duplicate posts that keep happening? I'm trying to delete mine...
  • Duplicate posts
    Any suggestions for avoiding the duplicate posts that keep happening? I'm trying to delete mine...
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top