Discuss Switch within a ring circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

so spurring of the switches to a single socket and maintaining the ring through the switch - is that allowed?
Why two switches- because he's planning to have a sink in between the applainces.
 
Last edited by a moderator:
so spurring of the switches to a single socket and maintaining the ring through the switch - is that allowed?
Why two switches- because he's planning to have a sink in between the applainces.

TBH, I can't see a problem with this setup. My only concern might be that the switches are rated for 20A so would that mean the input terminals are rated st 32A? There has been a debate about this with grid switch assemblies.
In practice, the loading is not going to be anywhere the rating of the protective device. So as stated elsewhere, A 20A DP switch feeding a BS1363 unswitched socket outlet would look reasonably pleasing.
 

Reply to Switch within a ring circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
668
The old thread, that our friend hijacked, is here 2 dimmers on 2 way switching -...
Replies
2
Views
864

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top