Hi, hpoe some one can shed a bit of light on this subject.
Am i able to install a switched fcu in a shower room.
The fcu is more than 0.6m away from shower tray and is feeding a towel rail.
It is also rcd protected.
Seems to be a bit of a grey area to me.
Many thanks.
 
Does the towel rail have its own controls in order to change to a non switched FCU?


Sent from my iPad using Tapatalk - Couple a' Tools
 
Last edited by a moderator:
Can the FCU be fitted in an adjacent room?


Sent from my iPad using Tapatalk - Couple a' Tools
 
Last edited by a moderator:
not allowed . see 701.512.3
 
Hi, hpoe some one can shed a bit of light on this subject.
Am i able to install a switched fcu in a shower room.
The fcu is more than 0.6m away from shower tray and is feeding a towel rail.
It is also rcd protected.
Seems to be a bit of a grey area to me.
Many thanks.

Why is it a grey area?
 
how do i start a new thread please?
click on "forum" ( top left). choose appropriate forum for your thread. then click "post new thread". don't forget title.
 
Am i able to install a switched fcu in a shower room.

only way is to install an unswitched FCU, with switching either outside the room or a pull cord switch.
 
yes it can but already wired in as customer inssted they would be switch from the heater.
oh well more time more money.
 
I agree with Telectrix. 701.512.3 complies with 13a outlets no less than 3m from zone 1 boundary on a 30a RCD so will have to be in another room. As you said though, more money lol


Sent from my iPad using Tapatalk - Couple a' Tools
 
Last edited by a moderator:
some say you can some say you cant.

If you are the one doing the design, installation and notification you need to decide for yourself as if it all goes txts up you'll be in court answering for your actions.

IMHO it should be outside the room.
 
quote: in zone 2. switchgear,accessories incorporating switches or socket outlets shall not be installed.......
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
switched fcu in shower room.
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
26

Advert

Thread statistics

Created
palace dave,
Last reply from
TPES,
Replies
26
Views
4,468

Advert

TrueNAS JBOD Storage Server

Back
Top